I have a 1762-IF2OF2 and I would like to connect a temperature transmitter giving 4-20mA. What determines whether it is 3277-16383 and 6241-31202 in the SCP. I get 3167 in by 4 mA
 
Ok. Maybe I am stupid :) But I do not understand. I have a SCP with Indput I: 1.0
Min 6241
Max 31206
SC min 0
SC max 100
F8:0 ....

But it is not the right value I get up
 
Min 6241
Max 31206
SC min 0
SC max 100
F8:0 ....

But it is not the right value I get up

This will not work. 6241...31206 is not a valid range for this module.


Referencing the manual the rdrast posted for you:

Make sure that the DIP switches are ON (default) for Current. (Page 8)

Go to the advanced I/O configuration for that module in RSLogix 500. There you should be able to select how each channel is scaled. (Page 14)
Raw/Proportional 0...32760
Scaled for PID 0...16380

All of this information is available in the AB manuals.
 

Similar Topics

so i want to use an analog output card, 1762OF4, and send a 4-20ma signal to a vfd for speed control, ill set the 4-20ma scale in the vfd from...
Replies
4
Views
1,553
Hello, I'm working with a 1747-NI4 analog input module (for the first time) on a SLC503 processor. I noticed in the IO configuration within...
Replies
13
Views
4,762
Hello all, I'm having an issue displaying the value I'm getting from a PFC to display on my Red Lion G307..... and before anyone says it...I...
Replies
1
Views
2,122
Quick question for you guys. I'm a little confused about something. I have a 1762-IF4 analog module and a pressure switch wire to it. The...
Replies
2
Views
1,940
Could someone tell me which of the available tags in a 1769-IF8 analog module is typically used for the output of an SCP instruction. I am...
Replies
66
Views
11,948
Back
Top Bottom