Hojland Member H Join Date Oct 2006 Location Langå Posts 203 Feb 22, 2010 #1 I have a 1762-IF2OF2 and I would like to connect a temperature transmitter giving 4-20mA. What determines whether it is 3277-16383 and 6241-31202 in the SCP. I get 3167 in by 4 mA
I have a 1762-IF2OF2 and I would like to connect a temperature transmitter giving 4-20mA. What determines whether it is 3277-16383 and 6241-31202 in the SCP. I get 3167 in by 4 mA
rdrast Lifetime Supporting Member Join Date Apr 2003 Location South Carolina Lowcountry Posts 5,544 Feb 22, 2010 #2 Whether or not it is set up as "Scaled for PID". http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1762-in005_-en-p.pdf See page 14.
Whether or not it is set up as "Scaled for PID". http://literature.rockwellautomation.com/idc/groups/literature/documents/in/1762-in005_-en-p.pdf See page 14.
Hojland Member OP H Join Date Oct 2006 Location Langå Posts 203 Feb 22, 2010 #3 Ok. Maybe I am stupid But I do not understand. I have a SCP with Indput I: 1.0 Min 6241 Max 31206 SC min 0 SC max 100 F8:0 .... But it is not the right value I get up
Ok. Maybe I am stupid But I do not understand. I have a SCP with Indput I: 1.0 Min 6241 Max 31206 SC min 0 SC max 100 F8:0 .... But it is not the right value I get up
blamb Member B Join Date Jan 2010 Location Casper, WY Posts 126 Feb 22, 2010 #4 Hojland said: Min 6241 Max 31206 SC min 0 SC max 100 F8:0 .... But it is not the right value I get up Click to expand... This will not work. 6241...31206 is not a valid range for this module. Referencing the manual the rdrast posted for you: Make sure that the DIP switches are ON (default) for Current. (Page 8) Go to the advanced I/O configuration for that module in RSLogix 500. There you should be able to select how each channel is scaled. (Page 14) Raw/Proportional 0...32760 Scaled for PID 0...16380 All of this information is available in the AB manuals.
Hojland said: Min 6241 Max 31206 SC min 0 SC max 100 F8:0 .... But it is not the right value I get up Click to expand... This will not work. 6241...31206 is not a valid range for this module. Referencing the manual the rdrast posted for you: Make sure that the DIP switches are ON (default) for Current. (Page 8) Go to the advanced I/O configuration for that module in RSLogix 500. There you should be able to select how each channel is scaled. (Page 14) Raw/Proportional 0...32760 Scaled for PID 0...16380 All of this information is available in the AB manuals.
Mickey Lifetime Supporting Member Join Date May 2003 Location Palmdale,Ca Posts 10,659 Feb 22, 2010 #5 And here are some pretty pictures for you. ( forth a 1000 words I think)
Hojland Member OP H Join Date Oct 2006 Location Langå Posts 203 Feb 22, 2010 #6 thanks guys...that was all i needed