SIEMENS S314C2DP, STOP when go Online with PC

italo2008

Member
Join Date
Feb 2009
Location
Padova
Posts
95
I have a siemens 314c 2dp cpu and some profibus slaves. When I try to go online with PC, CPU goes in STOP. I tried to go onLine via Profibus and via Ethernet but each time CPU goes in STOP modality... In diagnostic I see that STOP is due to access erron on peripheric...

anyone can help me?
 
Last edited:
Hi Italo,

as a remedy you can download the OB122 to prevent CPU from stopping. But the reason for your problems is that you lose connection to some of the profibus slaves.

Do you have a separate ethernet module on your rack when you say that you tried to connect also with ethernet?

Does the CPU stay on when you download OB122?

What does the diagnostic buffer say then? I mean does the IO access error go away after a short time?

Maitomies
 

Similar Topics

The past week we received a new piece of equipment from Germany which utilizes siemens controls. Typically in our company we use A.B. controls for...
Replies
9
Views
159
Hello I have a s7-1200 and I would like to read the tags present in this controller with my controllogix controller. The two controllers don't use...
Replies
5
Views
141
Hi need help why this “failure 5 emergency stop “ appears at every startup in the morning ? Have to shut off main switch at least 10 times on...
Replies
19
Views
300
i have two plc 1. s7-1212dc/dc/dc ip; 192.168.0.1 2. s7-1500 1513-1pn ip; 192.168.3.2 i need to get data from plc1 to plc2. any idea how to do...
Replies
5
Views
112
Hi everyone hope you'll well. Is it possible for me to download a Crack version of tia portal v13..sorry to say this but the software is very...
Replies
5
Views
198
Back
Top Bottom