Slc500 - Modbus Protocol

robertopsilva

Member
Join Date
Oct 2003
Location
Fortaleza - Northeast of Brazil
Posts
12
I´m trying to comunicate an SLC500 CPU 5/03 with an energy measurement device through Modbus protocol. Is there a way to do that without using a protocol converter such as DF-1/MODBUS or DH485/MODBUS? Maybe configuring the serial RS-232 Port (Channel 0) to ASCII protocol? Any help would be greatfull.
 
No

No, you're not going to get the data in through the SLC's serial port. I'm not even sure if Modbus and DF1/RS-232 are electrically compatible, never mind the protocol translations.

So you have two choices: an external protocol converter, like SST's XLinks, or an internal protocol converter, like ProSoft's Modbus modules.
 
I used a card once that plugged into the 500 rack. The only numbers I got is 3150MCM communications card. If your interested I could dig deeper. It converted modbus RTU to SLC50 registers I found it by- chance-by-golly on the internet last year. The customer screwed us so we send the card back and never got the chance to use it. The documentation was real good.

-----------------------------------------------------------------

" Protocol jumping .... COOL STUFF"
------------------------------------------------------------
 
KEN - That is the Prosoft card. We use it in systems so that the SLC500 can give MODBUS commands to some Control Techniques servo controllers. It's a real PITA to set up using the M registers but once I got it going I never touch it. It does what it says, mostly automatically.
 
If you're already using DeviceNet, you can use a DeviceNet/Modbus converter for 300 to 500 bucks. It's cheaper and easier to use than a 3150-MCM and won't take up a slot.

It's my favorite way to interface with Modbus-based slave devices, though they haven't caught with everybody the way I like 'em.

WRC makes my favorite 1782-JDM. www.wrcakron.com
 

Similar Topics

Hi all, I am having some issues with modbus values. I am using a Floboss 107 as a Modbus Master, polling data from a SLC 5/04 that has prosoft...
Replies
1
Views
2,250
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
254
can the slc500 5/05 send a email and text over Ethernet ?
Replies
3
Views
185
Hello, did anybody know, if there exist an converting cable like the1492-CM1746-M01 (for an 1746-IB16 to an 5069-IB16), for an 1746-HSCE to an...
Replies
3
Views
389
Customer is buying several spare 504 CPU's to have one handy when there's an issue with the ones in operation. Having them on the shelf for years...
Replies
15
Views
2,830
Back
Top Bottom