OK, I'm stumped- I have a problem with a 120 volt output staying on on a particular AB PLC 5/20 Remote rack- older system, output card is Cat#1771-OA, eight bit 120 volt output, turning on some pneumatic solenoids, Outputs 0 and 3 stay hot even though looking at the program they are OFF. Swapped cards, same problem, Using the PLC to force the output ON lights the output indicator LED on the card, forcing output OFF turns the LED on the card off, either case the output is on, voltage stays at 120VAC. Swapped the Rack, suspecting a backplane issue, still have the same problem! Looking at the data table, the output should be off, but I have voltage! Disconnected all field wi=ring from this particular rack, connected a seperate 120 volt source to the problematic card, still have two outputs that stay on, no LED. Does anyone have any ideas? checked backplace power supply, looks Ok at 5.01 VDC
 
Common

Yes, I checked bact to the transformer supplying PLC power, Looks like neutral is tied to ground OK, same potential. I did see on an older post that Ron suggested my load might be too low, I'll try a load resistor in parallel with my solenoid valve, but I sure thought the solenoid would be enough of a load by itself. Thanks for the response,
 

Similar Topics

Preface: Kinda long, so I made section titles Intro: I just want to see if anyone here has seen anything similar. A PLC5-40 series C enhanced...
Replies
3
Views
364
I had a customer ask me to investigate what state a digital output would be in a PLC5 if the the processor faulted or was put in program mode...
Replies
1
Views
1,182
Hey guys, I have a problem that is puzzling me on a PLC 5 system. I am using a 4-20mA analog output (1771-OFE2/B) straight to a Powerflex 4m...
Replies
7
Views
3,684
Hi all, I have a PLC5 rack that is actually full(No place for an aditionnal card). The rack has a couple of spare inputs on 1771-IFE cards and I...
Replies
5
Views
3,680
Hi, I will start with an apology because I'm so new to this that the next question will sound really stupid. I'm using a PLC5 a&b at home for...
Replies
10
Views
2,966
Back
Top Bottom