figured it out
Thanks very much for your reply. I didn't put all of the details because it really doesn't matter since NONE of the quickpanels natively support ANY compactlogix processors via ethernet or RS232. This was according to GE support, and because you can't select compactlogix under processor type in the latest software (proficy machine edition 6). I didn't contact Rockwell support because it wasn't their issue. Here's what I had to do.
1. Use native drivers NOT OPC drivers like tech support says
2. Under native, choose DF1 and then select ControlLogix as the processor because CompactLogix is not even an option
3. In RSLogix 5000, set the system protocol do "DF1 point to point" not "DF1 Slave" like GE Support says.
4. Use Tag Names NOT PLC5/SLC emulation like GE Support suggests
Also, tech support told me I needed a straight-through cable which was only partially true. I had to make my own cable because a simple straight-through one doesn't cut it. Look up the pinouts for a HMI-CAB-C52 cable.
Hopefully this helps someone else down the line!
and I'm not using ethernet because the QuickPanel is supposed to be a back-up to the iHistorian server. There's no point in having it there on ethernet as a backup if the switch or ethernet port on the PLC fails.