Hello,

We have a plant were we are using siemens CPU313C with a CP342-5 card set up as a passive slave. The master is a Kongsberg controller which is part of a PMS.

I am using FC-send and FC-receive to communicate with the master. The master is using the GSD file for the CP card.

This works nice at the most of the time, but occasionally the Kongsberg primary controller changes from master to redundant controller. At that point I get the status value of 5 on my DP receive block and all the values I receive are set to 0.
The Kongsberg system is receiving the data from my DP send block, no problem.

After reading the documentation for DP protocol, I understand that the value 5 means that the master is in clear mode and the slave goes into fail safe, which is defined by the GSD file.

If I restart my CP card, then everything is working fine afterwards.

What I don't understand is why I have to restart my card when the master is runnning fine again. Shouldn't the slave go back to normal operation which is value 1 on the DP receive?

Has anybody seen this before and knows if something has to be adjusted? watchdog time etc... ??

Appreciate any responses...

brg
Andreas
 

Similar Topics

Hello, I am in possession of a WAGO PFC 200 750-8216 which I was successfully able to set up as a Modbus RTU Master to a slave device using...
Replies
0
Views
72
Dose anyone have experience with Beckhoff FC3121 profibus master PCIe card connected to Siemens CP342-5 as a profibus slave? The data retrieved...
Replies
17
Views
4,783
Good morning, I am looking to establish a communication between one Profibus master and one Profibus slave. I downloaded the Profibus Master...
Replies
58
Views
14,456
Hi all. Spending a couple of weeks testing some systems in Norway. Some of the systems have drives controlled by PROFIBUS. Instead of unpacking...
Replies
9
Views
4,187
Experts! Advice required S7300 CPU 2 DP 315 Master Slave Profibus.(2 CPU) In My application I have to send data from Master to slave and slave...
Replies
0
Views
1,938
Back
Top Bottom