Panelviewplus compact 1000 and SLC5/05 Comms issue

Matthewn

Member
Join Date
Mar 2010
Location
Galway
Posts
10
Hi All,

I'm having difficulty establishing communication between a panelview plus compact 1000 and an SLC 5/05(processor 1747-L552). I can communicate fine with both the SLC and PV through my laptop using serial connection and DF1 driver but I cannot get the runtime application to register values from the SLC at runtime. I'm using factory talk view ME V 5.10 and I have created a shortcut to the SLC in the runtime tab of rslinx enterprise under a DF1 driver which I added. All the comms settings match the SLC comms settings and I even selected auto configure to eliminate this as a possible cause. The device tree which I selected under the DF1 driver in the runtime tab of rslinx enterprise looked like this - DF1P2P, Serial-DF1 > PCCC DH485 Devices > SLC DH485 devices 1747-L552E, SLC-5/05 Processor w/32k. And I selected this SLC 5/05 as my shortcut. But nothing. I'm using the same lead as I used for programming the panelview to talk with the SLC, and from what I read this seems ok. Am i doing something terribly novice here?? Could anyone shed some light??

Matthew.
 
First make sure you are using the cable 2711-NC13 between the 5/05 and the PV (2-2,3-3 and 5-5 is the pinout)
Second it's 100% easier to communicate by using the ethernet port, cause as soon as you're studio is able to test your application, you can copy the design shortcut to the runtime, and woila!!!
 

Similar Topics

Hello Everyone, I am setting up an Information message in FactoryTalkView ME. I'm just using the default information display. I want to make it...
Replies
4
Views
843
Hello to the community, I am new to Rockwell and I have a small problem with a PvP1000(2711P). Some buttons in the same screen are not...
Replies
4
Views
2,328
Hello, I have a PV+ 1000 that I am unable to access the config screen on. All I want to do is upload the .mer that is currently running. I tried...
Replies
21
Views
4,896
If you were to take a Panelview Plus, mount that in an enclosure that is purged by a purge unit that takes the environment from Class 1 Division 1...
Replies
15
Views
5,627
So im working on a little something i was hoping to get some advice on. I have a PanelviewPlus 7 that will be using the MECSVLog ActiveX on to...
Replies
2
Views
1,241
Back
Top Bottom