What determines if a FB can be used as a multi instance?

According to Berger "Prerequisite is that both the calling function block and the called function block have block version 2, that is, that both have "multiple instance capability"."

What does this mean and how do you check for "block version 2"

I have an old block that will not allow me to use it as a multi and wondering if there is a change I can make or if I have to redo it.

Thanks,
-Joel
 
I may be able to get to that a little later. I was just wondering if there was a simple answer for why not all FB's can be Multi Instance.
 
To convert your FB to multi-instance you must first generate the source code for the block.

Remove the line CODE_VERSION1

Re-compile the block.

Code:
FUNCTION_BLOCK FB 1000
TITLE =
VERSION : 0.1
[B]CODE_VERSION1[/B]
BEGIN
NETWORK
TITLE =
END_FUNCTION_BLOCK
 
I created the source of one of the FB's I was trying to multi use. When inside I couldn't find the "CODE_VERSION 1" line.
So I then right clicked on the FB in simatic manager and went into object properties. Upper right corner says it is "multi use capable" But when I put it into another FB, highlight it, then select edit->block call my option for "Change to multiple instance call" is grayed out.

Any other ideas?
 
See post#2

Late thought - is the interface empty for the FB you are trying to use ?
 
Last edited:
I have been trying for a while to get the FB's into a library. Figured out how to create a library, then I copied the FB's in but it keeps on having issues with FC calls being changed to Call/End calls and some other issues. I think I'll just have to leave the FB's with there individual DB's

No the interface is not empty.
 

Similar Topics

Hello all. I have an ESA HMI that is connected to a Simatic S7-300 (CPU312). I have uploaded the program from the PLC which is written with Step7...
Replies
6
Views
1,439
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
686
Hi to all, Our company does not usually use Siemens PLCs, but have a press with one in it. We are trying to change the IP address in our Simatic...
Replies
2
Views
1,066
G'day guys, I am setting up a s7-300 as a test rig for the workshop and when I downloaded the PLC is not going into run mode, I keep getting a...
Replies
35
Views
5,211
I am trying to write just MSEC to S7 300 Controller date/time using OI.SIDIRECT Aveva communication driver? The old HMI (WINCC) tag is assigned...
Replies
1
Views
1,059
Back
Top Bottom