CPM2A Omron PLC question

mraj2001

Member
Join Date
Jul 2009
Location
Jabalpur
Posts
20
Hi,
I have a CPM2A PLC setup for a machine. There is an rotary incremental encoder connected to the PLC at input 0.00 (A+ terminal of encoder) and at 0.01 (B+ terminal of encoder). When the encoder rotates I can see LED switching at these inputs. But when I connected my PC to PLC and look in the program but I am unable to see these inputs in ladder logic. Can you explain me how the pulses of encoder are counted in the program. Which instruction may be used


mraj2001
 
High-speed Counter Inputs
Inputs IN00000 through IN00002 can be used as high-speed counter inputs, as shown in the following table. The maximum count frequency
is 5 kHz in differential phase mode and 20 kHz in the other modes.
Input Function
Differential phase mode Pulse + direction input mode Up/down input mode Increment mode
IN00000 A-phase pulse input Pulse input Increment pulse input Increment pulse input
IN00001 B-phase pulse input Direction input Decrement pulse input Normal input
IN00002 Z-phase pulse input/Hardware reset input (IN00002 can be used as a normal input when it is not used as a high-speed
counter input.)

Interrupt Inputs

CPM2a MANUAL

yUO WILL ALSO NEED TO ENABLE THE HIGH SPEED COUNTER UNDER SETTINGS ON THE LEFT HAND SIDE AT THE PROJECT TREE
 
Last edited:

Similar Topics

hey anyone, I'm a student from Indonesia.. I have a project, It is about how to send and receive data by serial communication between PLC Omron...
Replies
2
Views
2,115
Hi All, need a little help in here.I never program PLC before but at the moment, I am task to backup PLC program on our machines which is using...
Replies
2
Views
5,671
Dear Experts Help me to upload plc program from Omron PLC CPM2A to laptop. CPM2A name is not in the device type setting list of...
Replies
1
Views
3,165
Dear PLC Experts, I am trying to go online with Omron Sysmac CPM2A PLC with CX-Programmer V 6.0 on Windows Vista Operating System. It gives...
Replies
7
Views
9,713
Hello, I hope someone can help to resolve the current issue that I have now. I am using OMRON CPM2A PLC connected to the desktop PC so that it...
Replies
7
Views
36,159
Back
Top Bottom