Do anyone know a good universal programmable converter from any standard protocol like Modbus RTU or Profibus DP or maybe Ethernet TCP to Backnet serial


I would like to convert an Emerson Unidrive to Backnet and this drive (AS far as i know) just gives standard comm protocol with option modules
 
are you using the Ethernet model or the serial?

i just see general info that doesn't tell what is comming in to be transformed to Backnet in the spec
 
It can do both. It comes standard with 1 RS232 port, 1 RS485 port, and 1 ethernet port.

I assume that your Modbus would come into the RS485 port. You can then go BacNet IP out the ethernet port, or buy the expansion card that will give you a second RS485 port for BacNet MSTP (serial).


...or you can bring your Modbus RTU in through the RS232 port, but that's probably not the best way to do it.
 
Last edited:
You will need to get a list of Modbus addresses for the data coming in and map them to BacNet addresses for the data going out.

The 'program' file is transferred to the Datastation via USB cable.
 

Similar Topics

Hi all Trying to remotely connect to a TIA Portal PLC. I can ping it without a problem but can't get my software to connect. I've opened port...
Replies
8
Views
282
I’m working on getting a Parallel Redundancy Protocol PRP system set up in a lab situation. The L73 PLC is in rack 4. 3 io racks are 1,2,3. I...
Replies
6
Views
691
Does anyone have information or documentation regarding the protocol used in Rockwell's Remote IO, and how the physical layer of the network...
Replies
5
Views
877
Hi everyone, I've got to interface 4 x Mitsubishi Q series PLC's with an Allen Bradley Compact Logix PLC using a Red Lion Data Station DSPLE000...
Replies
1
Views
488
Dear Experts , I have a system which contains 10 PLCs (1214C CPU) each PLC with GSM module (Teltonika RUT955) and 2 SCADA PCs at different...
Replies
2
Views
797
Back
Top Bottom