Looking for any recommendations, as I have very little experience with modbus.

I have 4 units, each with 2 stand alone single loop controllers that have modbus capability. I need to get data from these controllers to our BAS system.

My initial thought is to network the 8 controllers and connect them to a Micrologix 1100, then our OPC server can get the tag values over ethernet.

The thing is, the units are portable in theory,(though I don't expect them to be moved much if at all) so if I could keep them separate, that would be better. But I don't want to put in 4 ML1100. My question is, is there a cheaper way to get the modbus data to a remote OPC server. I know the PLC will do it, but is it really necessary? There is no control required, only monitoring.

The bridges I've seen are in the same price range as ML1100, and I'm not clear what would act as the master if no PLC is there?

Thanks for any suggestions,

Rob
 
Not enough information has been given.

What sort of physical communications do your remote devices support? RS-232, RS-485, Ethernet? That will make a huge difference in the answer to your question.
 
I am guessing that the devices are serial and you want to convert to ethernet?

check with lantronix or digi. both are solid options and very easy to setup.

also, if your devices support rs485 you can network them all together on a 485 bus then connect them to a single lantronix or digi.

another option if the devices only support rs232 and are within 50 or so feet of each other is to use a black box splitter, which will allow you to tie all of the devices in then use a single digi or lantronix to collect the data.

post what you have for a better description.
 
Yeah, I don't think I can get any lower cost than that, just thought I'd ask. I don't think I will need the AIC for the 1100 though, if we use the 1763-NC01 cable.

Thanks again,

Rob
 
Yeah, I don't think I can get any lower cost than that, just thought I'd ask. I don't think I will need the AIC for the 1100 though, if we use the 1763-NC01 cable.

Thanks again,

Rob

You're right. All you need is the NC01.
 
I wouldnt use a 1100 just for this. thats overkill. wire the 485 devices together, give them each a different rtu address, put a 120 ohm resistor on each end, and use a lantronix or digi or any other ethernet to serial converter. the only way i would use the micrologix would be if you wanted a hardware firewall, or if your opc server only handled ab protocol.
 
I looked at the Digi One IA, and it's about $150 less than an ML1100, so could save a little. But that's where my ignorance of Modbus is a problem. So my 8 devices are slaves and are daisy chained to a serial/enet converter. What is the master, i.e. what initiates data transfer from the devices?
 
I looked at the Digi One IA, and it's about $150 less than an ML1100, so could save a little. But that's where my ignorance of Modbus is a problem. So my 8 devices are slaves and are daisy chained to a serial/enet converter. What is the master, i.e. what initiates data transfer from the devices?

Your OPC server.
 
OK, thanks Mickey, that makes sense. So a tag configured in the OPC server with Modbus TCP driver should grab the data. Sorry, like I said, haven't worked with modbus much at all.
 

Similar Topics

I'm currently moving ahead on the proportional controls for a set of cooling vats. I'll be using Solo SL4824-CR temperature controllers to provide...
Replies
13
Views
5,519
Hi Had two modbus related work the last week, and can see that I need a software to capture the data that are sent between the communicating...
Replies
15
Views
46,337
Hi Everyone, i was hoping for a little help with this module. i have data that needs to be read from a different plc through the Modbus plus...
Replies
9
Views
85
I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
5
Views
145
Dear All, i am trying to connect Danfoss inverter with s7 200 cpu 226.but microwin shows following error at DATA Ptr.i assigned different VB...
Replies
1
Views
46
Back
Top Bottom