Stationmaster
Member
Hello all, I have been using Hitachi drives for the last few years, have installed about 40 or 50 in all types of machinery, mostly pumps. So when I was asked to retrofit an existing pumping system with a new VFD, I had no worries. The previous VFD was an ABB , the new one is a Hitachi L300P, 480 vac, 75hp. The signal in question is the analog speed reference, 0-10v.
The VFD "hunts" at a frequency of about 2 cycles per second.
I have been in touch with the mfg of the pumping system controller, and he shared info about the PI loop, and tuning the variables. I have tried a variety of combinations, some resulting in less or no "wow", but completely useless as far as following the pressure, correcting for disturbances, etc.
I have set the accel and decel in the drive, bit by bit, with the same result: if I get rid of the "wow", the perfomance is deplorable, or almost non-existant.
The controller mfg told me that they know their system has that tendency, but they just tune it out with the "analog filter" in the ABB, by setting it to average for 2 seconds. So I found the "analog filter" in the Hitachi, which sets from 1 to 30... and set it to the max, 30 (which represents 30 samples taken, then averaged before loading the value as the speed reference), but whatever it is it isn't enough.
The customer SWEARS it never DID that before I put in the new VFD. I have talked to KELE and they say they can make me an "external analog filter" but I have to tell them what "time constant" I want. I'm going to the site tomorrow with an IDEC PLC, (my usual brand) and an analog i/o card.... so I can MAKE an averaging circuit with settable time constant, and I can determine an optimal range.
I KNOW there will be questions... I CAN'T have included absolutely EVERYthing... But I have tried to share what the problem is (the "wow" or "hunting" at about 2 x sec across the entire ranges of pressures and flows) and all the things I've tried thus far.
If there is an easier or more straight forward way.... I'm ALL ears.
ANY comments from people with actual experience in this area will be appreciated....
Thank You,
Stationmaster
The VFD "hunts" at a frequency of about 2 cycles per second.
I have been in touch with the mfg of the pumping system controller, and he shared info about the PI loop, and tuning the variables. I have tried a variety of combinations, some resulting in less or no "wow", but completely useless as far as following the pressure, correcting for disturbances, etc.
I have set the accel and decel in the drive, bit by bit, with the same result: if I get rid of the "wow", the perfomance is deplorable, or almost non-existant.
The controller mfg told me that they know their system has that tendency, but they just tune it out with the "analog filter" in the ABB, by setting it to average for 2 seconds. So I found the "analog filter" in the Hitachi, which sets from 1 to 30... and set it to the max, 30 (which represents 30 samples taken, then averaged before loading the value as the speed reference), but whatever it is it isn't enough.
The customer SWEARS it never DID that before I put in the new VFD. I have talked to KELE and they say they can make me an "external analog filter" but I have to tell them what "time constant" I want. I'm going to the site tomorrow with an IDEC PLC, (my usual brand) and an analog i/o card.... so I can MAKE an averaging circuit with settable time constant, and I can determine an optimal range.
I KNOW there will be questions... I CAN'T have included absolutely EVERYthing... But I have tried to share what the problem is (the "wow" or "hunting" at about 2 x sec across the entire ranges of pressures and flows) and all the things I've tried thus far.
If there is an easier or more straight forward way.... I'm ALL ears.
ANY comments from people with actual experience in this area will be appreciated....
Thank You,
Stationmaster