OK, let me paint my picture before I get to the question. We have a pumping system that is connected to the customer's wireless Ethernet network. The customer supplied the IP addresses for 1 HMI (PV+), 2 drives (Powerflex 400), 1 PLC (CompactLogix), the radio, and a separate device in another panel. We have a 6 port switch in our panel connecting them all.
Recently, one of the drives' 22-COMM-E has started "faulting". When it happens, we get the following lights:
Port: Steady Green
Mod: Flashing Green
Net A: Flashing Red
Net B: Off
It will stay in a fault condition (actually the PLC program is causing the "fault" as it is monitoring the IO module's FaultCode) for several minutes, then re-connect to the network. This is causing problems, as you could imagine.
So if I am interpreting the manual correctly, this looks like a case of too much network traffic, or too slow. The RPI for the drives is set to 400ms. My question is, if there is a Gateway configured in the PLC, and the gateway is remote to the panel on the wireless network, does the drive's ethernet traffic have to go out the PLC, through the wireless, to the gateway, and back through the wireless, to the drive? Or will the packets stay local to the switch in our panel? Would further increasing the RPI alleviate the problem?
As always, Thank you in advance.
Recently, one of the drives' 22-COMM-E has started "faulting". When it happens, we get the following lights:
Port: Steady Green
Mod: Flashing Green
Net A: Flashing Red
Net B: Off
It will stay in a fault condition (actually the PLC program is causing the "fault" as it is monitoring the IO module's FaultCode) for several minutes, then re-connect to the network. This is causing problems, as you could imagine.
So if I am interpreting the manual correctly, this looks like a case of too much network traffic, or too slow. The RPI for the drives is set to 400ms. My question is, if there is a Gateway configured in the PLC, and the gateway is remote to the panel on the wireless network, does the drive's ethernet traffic have to go out the PLC, through the wireless, to the gateway, and back through the wireless, to the drive? Or will the packets stay local to the switch in our panel? Would further increasing the RPI alleviate the problem?
As always, Thank you in advance.