I have recently received a piece of equipment from an oem with an Allen Bradley Pico controller. I have pulled wires and set it up to run using a 1756-OW16 output card to drive three inputs from a supervisory Controllogix processor. The problem is the outputs have a small leak current that activates the inputs on the Pico controller even when the outputs are off. My quick fix was to put a small light bulb as load to bleed off the stay current and pull the voltage to zero. This has worked up to now, but this is not the best solution. What I think I need is a high resistance load resistor to pull down the leak current. Does anyone know what value/wattage I should use for this?
 
OW16 is a relay output card so I don't see how you could be getting any leakage current. When the output is off, there is a mechanical break in the circuit. Is your control voltage 24VDC?

If I need to pull down an output or input, I typically use a 1/4W 10K resistor. The optoisolators on PLC inputs generally operate in the <10mA range, so this is more than sufficient.
 
Thanks for posting the details on relay contact outputs that leak current. That was news to me. Who'd a thought . . . .?
 
Thanks for posting the details on relay contact outputs that leak current. That was news to me. Who'd a thought . . . .?

That got me with a flex relay output module once. Spent a couple hours troubleshooting before I got the manual out.
It ran fine for a few years with nothing but solenoid loads. We then connected an electronic strobe light, it worked fine when the relay was pulled in
but when the relay was open the light would blink about every 8 min. Something in the light was apparently charging up thru the leakage. I thought how could this be, its a "relay".
 
Last edited:

Similar Topics

I cannot find anything anything in the manual for a load resistor, does this PLC not have any built in? Is it a dipswitch setting?
Replies
4
Views
1,880
I am running CCW 13 trying to upload to a micro 820 vers.12 I get an output message OPC server is unable to load project controller. Please help!
Replies
5
Views
224
Hey guys, I have to take an upload of a program on an S71200 PLC to change a hardware config option and then redownload the program with this...
Replies
3
Views
110
Please help me How to B&R 7CP476.60-1 upload program Backup and download which program should I use. Pvi transfer tool.? And how. Thank you
Replies
0
Views
87
I HAVE A OLD MESSUNG HMI AND I WANT TO UPLOAD A PROGRAM FILE FROM IT TO A USB PENDRIVE WITHOUT USING PC OR SOFTWARE...WHAT SETTINGS I HAVE TO DO...
Replies
2
Views
74
Back
Top Bottom