Hi,

Just want to ask those experience user, do I need BT for 1746-NO4V or any 4 channel analog module for slc 500 in a RIO setup using 1-slot addressing?

Thanks.

Regards,
CK Chew
 
Can you please tell us more about your set up.

Are you using a 1747-SN scanner module with a 1747-ASB in the remote chassis??

If this is true then the 1746-NO4V module can be addressed either using BT or with Discrete I/O. This is selected with SW3-7 on the ASB modules.

If you have only one analog module in the remote chassis, then Discrete I/O may work fine and requires no extra programming in the SLC, but it does take up more words in the I/O image. Specifically the 1746-N04V will take up 4 words of Output image in the 1747-SN scanner.

The advantage of BT mode is that it only uses up one byte of the I/O image....but it requires more programming and the SN module will only transfer one BT per I/O scan. So if you have say five analog modules in the remote chassis, they will only be updated once every five I/O scans. (This might be perfectly fast enough for your application.)
 
Philip,

I'm running 1747-BSN in my local rack. In my local rack I've a pair of hot-back SLC 5/04.

In my remote rack I've this 1746-NO4V. I'm using 1-slot addressing. Require BT right?
 
Hi,

As I explained above you can do this with either BT ...OR discrete I/O image.

Which one you choose depends on how much spare I/O image you have in the 1747-SN/B scanner.

If you have plenty of spare I/O image then I suggest you use discrete I/O image transfer.

If there is not any spare I/O then use the BT.

All this is explained in Ch 3 of the 1747-ASB manual. It has all the details you need.
 

Similar Topics

Does anyone have a sample of a Block Transfer program for a Slc-500 C series Allen Bradly plc?? I would like to look at an example of how to write...
Replies
41
Views
12,956
Hi, I'm sorry if this question has been asked before, but just want to confirm that the discrete IO does not require Block Transfer, right...
Replies
17
Views
8,649
Hello there, I'm practically new to the PLC world, I'm quite familiar with Siemens TIA Portal but I'm currently tasked to program Schneider PLCs...
Replies
5
Views
1,860
Hi friends, I m new to plc programming and i don't know how to write data block in boolean method. I m needed to write data block to...
Replies
0
Views
1,687
Could some one show a simple example of how to use this block in order to generate a pulse of 500ms on and 500 ms off? I tried to do this but i...
Replies
1
Views
2,073
Back
Top Bottom