Can you please tell us more about your set up.
Are you using a 1747-SN scanner module with a 1747-ASB in the remote chassis??
If this is true then the 1746-NO4V module can be addressed either using BT or with Discrete I/O. This is selected with SW3-7 on the ASB modules.
If you have only one analog module in the remote chassis, then Discrete I/O may work fine and requires no extra programming in the SLC, but it does take up more words in the I/O image. Specifically the 1746-N04V will take up 4 words of Output image in the 1747-SN scanner.
The advantage of BT mode is that it only uses up one byte of the I/O image....but it requires more programming and the SN module will only transfer one BT per I/O scan. So if you have say five analog modules in the remote chassis, they will only be updated once every five I/O scans. (This might be perfectly fast enough for your application.)