Hi all.
I am supporting a collegue of mine who is onsite and I am assisting him remotely.
This is the case:
Main panel. Has 319-3PN/DP CPU. 1st DP port X1 is connected to many ET200S and 1 MM4 in the same panel. Works without problems.
Distributed panel, 100 m away. 2nd DP port X2 in main panel is connected to many ET200S and 2 MM4 in this panel.
Bus speed is 187.5k.
All MM4 have output chokes.
When we start the bigger of the two MM4 in the distributed panel, profibus net X2 goes on BF.
What we have checked:
Tightened all connections everywhere.
Checked that screen on motor cable is clamped to earth bus bar.
Checked that screen on profibus cable is clamped to earth bus bar.
Checked all Profibus connectors.
Checked earth to both main and distributed panel. Supply cable earth to both panels are connected to same earth star point.
Big MM4 has been replaced (!).
As far as it is possible, Profibus cables have been laid seperately from power cables.
Nothing of this helped or revealed anything.
Then we increased the Retry Limit in the Bus profile from 1 to 3. This made the BF disappear.
OK, it works so far, but I think that this is not an extreme case, and since everything is done properly, it should not be necessary to tweak the bus profile.
Any other ideas as to what we can check or do ?
I am supporting a collegue of mine who is onsite and I am assisting him remotely.
This is the case:
Main panel. Has 319-3PN/DP CPU. 1st DP port X1 is connected to many ET200S and 1 MM4 in the same panel. Works without problems.
Distributed panel, 100 m away. 2nd DP port X2 in main panel is connected to many ET200S and 2 MM4 in this panel.
Bus speed is 187.5k.
All MM4 have output chokes.
When we start the bigger of the two MM4 in the distributed panel, profibus net X2 goes on BF.
What we have checked:
Tightened all connections everywhere.
Checked that screen on motor cable is clamped to earth bus bar.
Checked that screen on profibus cable is clamped to earth bus bar.
Checked all Profibus connectors.
Checked earth to both main and distributed panel. Supply cable earth to both panels are connected to same earth star point.
Big MM4 has been replaced (!).
As far as it is possible, Profibus cables have been laid seperately from power cables.
Nothing of this helped or revealed anything.
Then we increased the Retry Limit in the Bus profile from 1 to 3. This made the BF disappear.
OK, it works so far, but I think that this is not an extreme case, and since everything is done properly, it should not be necessary to tweak the bus profile.
Any other ideas as to what we can check or do ?