Can someone tell me the correct way to filter an analog input to get stable readings on my HMI? We recently configured an input for motor amps and we want to filter it so that it is not jumping all over on the screen.
Thanks
 
The first place to start, is on the module property pages, the "Channel Configuration". Standard Logix 5000 analog input modules have both notch filtering, and digital low pass filtering on a per channel basis.

Second, you can use the old standby in logic:
Filt = (Unfilt - Filt)/Constant + Filt
where Constant can run from 5 to 100 or so, trigger that every 100ms or so.

Third, you can probably filter the value on the drive output.

But, do you really want it filtered? Is the signal actually that variant? I generally like to datalog and trend unfiltered, but display a filtered value for the operators.
 
Sorry, I hit my mouse before I completed my thought.

However, your last suggestion is what we are attempting to do, capture the raw input, meassage it somehow and send a filtered value to the HMI screen,

Dan
 
You could try using the moving average function in function block, or load up a FIFO on timed intervals in ladder and do the math to average how ever many samples you want.
 
Sorry, I hit my mouse before I completed my thought.

However, your last suggestion is what we are attempting to do, capture the raw input, meassage it somehow and send a filtered value to the HMI screen,

Dan

Uhhh, and? I listed three ways. The first and the third act on the actual raw I/O tag. The second requires that you read a new tag on the HMI, the 'Smoothed' value.

You want logic for method 2?


BST XIO MyTmr.DN TON MyTmr 100 0 NXB
XIC MyTmr.DN SUB RawValue SmoothedValue TempReal DIV TempReal 20.0 TempReal
ADD TempReal SmoothedValue SmoothedValue BND

I don't know what more to say.
 
It's one of the many digital implementations of a first order infinite input response low pass filter.

Keith

Aye, and has been used for many years by lots of people, primarily since its implementation is pretty simple in just about any PLC.

It has a secondary advantage of being easy to understand (functionally) with basic math skills.

There are many other, more developed and specific purpose filter algorithms out there, the Logix processors have 5 separate filter blocks, but honestly, I've never had to use them.
 

Similar Topics

Good day, I will have 2 L61 controllers in the same local rack.Is it possible that both controllers can own the same input module also located in...
Replies
7
Views
2,514
I have recently made a career change after 25 years of being an electrician. I am officially a junior automation controls programmer. I recently...
Replies
11
Views
365
Hi Guys, Hoping that someone could please confirm if the 1756-IF16/B is/isn't compatible with the 1756-L1 5550 processor(13.24). I'm sure I...
Replies
2
Views
103
Hello, I need help making a logic modification to a RS Logix 5000 program. I can email the program and give plenty of insight to it plus I have...
Replies
4
Views
2,201
Hey folks I was wondering how one puts shortcuts on the logic display for instructions. A few weeks back another programmer added them for me...
Replies
2
Views
971
Back
Top Bottom