i have a 1746-p2, i have 7 rack chassis with a slc 5/03 one input card and one output card, when i plug in the power suppy cord , the power supply blinks and turns off, i had this problem yesterday,some times it comes on some times it does not, so this morning it did it again, i put a new power supply and it did the same thing????? i changed every thing , processor, took cards out , changed rack???? help me plz, i also checked voltage on out let 125vac and also tried pluging in some where else , i got the same thing
 
Sorry to borrow your thread to post my question,
I have one remote io scanner 1747-SN installed on my SLC-500 chassis and connected to a remote flex i/o rack at remote location. Now, I want to add another flex i/o rack at the opposite location. That means I have to run a longer blue hose from the the existing flex i/o rack to the new one. From the manual, the network has to be in series. Is it possible to add another scanner card 1747-SN to my chassis for new connection? Do you have any better way to combat this? Thanks for your help.
 
Welcome to the Forum, Bob.

Generally you'll get better results starting a new thread, even if it's very closely related to a recent one (best to cite/link the previous thread).

To answer your question: the RIO network has to be in series, but not in sequence. The wiring is a parallel bus and the scanner can be anywhere.

Right now your network cabling is:

SN ASB
(T)........................................(T)



There's no reason the 1747-SN can't be in the middle of the daisy-chain:

ASB SN ASB
(T).........................|.......................(T)



The termination resistors (T) just have to be at the physical ends of the network; the Scanner does not have to be at the physical end of the network.
 
Last edited:

Similar Topics

I have a program that I've used 100 times. SQO settings: File N7:0, Mask 0FFFFh, Dest B3:1, Control R6:0, Length 8, Pos 2. Length & Position...
Replies
48
Views
956
Everyone, i am in the process of purchasing the Slc 500 version of software to support what we have and i have a question. Several of our...
Replies
9
Views
766
In a slc 500 plc I am trying to move data with out using a lot of moves. I want to move data from n7:1 to n7:2 and data that was in n7:2 to n7:3...
Replies
16
Views
1,355
Customer has a circa 2004 SLC-500 PLC. Fieldbus is a 1747-SDN DeviceNet scanner. Customer has SLC-500 file (.rss) with no comments. Has no *.dnt...
Replies
7
Views
553
After I tried wiring, I used computer program communication to read the PLC N value, but received a NAK signal. And the DL3500 CHA light keeps...
Replies
0
Views
424
Back
Top Bottom