RSLogix 5000 error: Module Fault (Code 16#0301)

nqn827

Member
Join Date
Aug 2007
Location
Livermore, CA
Posts
15
Hi All,
I'm getting the following error on the 1794-OB16P/A module:
Module Fault (Code 16#0301) Connection Request Error: Out of buffer memory.
Would anyone please tell me how to solve this fault? FYI. my setup consists of:
* A 1794-L34 with a 1788-CNC/A daughter card.
* Twelve nodes each consists of one 1794-ACN15/C, one 1794-IB16/A, two 1794-OB16P/A, and two 1749-IF2XOF2I/A.

Also, the problem went away if I cut down the number of nodes to eight.

TIA
 
I think this application is too big for the FlexLogix.

The 1788-CNC module and the 1788-ENBT modules support 32 CIP Connections maximum.

One Rack Optimized connection and two Analog module connections x 12 = 36 connections required.

I don't know if the FlexLogix could even handle this I/O with two 1788-CNC modules; the 32 connection limit is a maximum, and in my experience with medium RPI rates (10-20 ms) the -CNC module runs out of horsepower at about 10 scheduled connections.

I would recommend using ControlLogix as the controller for this system. The 1756-CNB supports 64 connections (40 to 48 in practice) and the 1756-CN2 supports 128 connections (and can run all the way to the maximum).
 

Similar Topics

Hi All, I've been pulling my hair out trying to fix this for a few days and need some advice. I have V19.01, v20.05, V21, V24, V30, V31, V32...
Replies
5
Views
396
Hi, I am trying to upload program from Contrologix 1756-L62 Controller using Rslogix 5000, Cpu's and modules are showing in Rslinx, upon...
Replies
3
Views
945
I've googled and searched for this error but can't see it anywhere. When I try to open this program I get the following. Error 0x8004201d...
Replies
12
Views
3,953
Hi all, I installed a RSLogix 5000 V20.04 to my Windows 10 system today, and it seemed everything is ok before I started it. The software gave me...
Replies
2
Views
2,930
fatal error in rslogix 5000 v20 Error 0x80042082 RxE_locale_changed_by_outside- the locale language Settings for RSLogix 5000 was changed
Replies
1
Views
1,994
Back
Top Bottom