Read Current from PowerFlex 4M

Join Date
Dec 2008
Location
Toronto
Posts
42
Can you get a Current Feedback reading to the PLC from a PowerFlex 4M drive? The PowerFlex 4M has a 22-COMM-E module installed. I am using a MicroLogix 1200 PLC. I currently get Logic Statis and Speed Feedback but no Current Feedback.
Thanks for your response.
 
Can you get a Current Feedback reading to the PLC from a PowerFlex 4M drive? The PowerFlex 4M has a 22-COMM-E module installed. I am using a MicroLogix 1200 PLC. I currently get Logic Statis and Speed Feedback but no Current Feedback.
Thanks for your response.

I haven't used the 1200 much, we have one in a piece of OEM Equipment. Ours doesn't have Ethernet, and I didn't think they came with Ethernet. How are you communicating with your PF4M over Ethernet? Perhaps you could post your RSS file (Zip it first), and it would give us a better idea of your setup.

Stu.....
 
Last edited:
Stu, my thoughts exactly...the ML1200 does not support ethernet. Maybe he meant 1100? or 1400? (Or there again, maybe there's an option available that I don't know about??)
 
Stu, my thoughts exactly...the ML1200 does not support ethernet. Maybe he meant 1100? or 1400? (Or there again, maybe there's an option available that I don't know about??)

He might be using something like a 1761-NET-ENI. I haven't set one up, but from comments I have seen on this list, they have very specific functionality, which I wouldn't think includes I/O. I guess we will have to wait for his reply.

Stu....
 
As an alternative to the above you could make use of thePF4M's on board modbus port. The only issue would be the ML1200 serial port only supports RS232 not RS485 (as does the ML1100/1400) so you would need a converter...

We have used modbus to read voltage/current/set+act frequency and full drive status.

Hope this helps.

Rob
 

Similar Topics

Hello all, I have some motors and I wish to read their current. Is there a device or module that can measure these and convert them to a standard...
Replies
9
Views
4,016
Hai Everybody, I have a doubt about How to read Voltage and Current values from a multifunction meter to Allen Bradley SLC 500 PLC through RS...
Replies
11
Views
3,007
Hi all, I'm trying to read the current output from an inverter into the PLC. The inverter has an analogue output configured for current. I've...
Replies
4
Views
1,968
Hello, I'm using a Danfoss drive FC302 connect via profidrive to a Siemens PLC 315. My problem is how can I read from the drive a current upper...
Replies
3
Views
2,184
I would like to be able to display on my HMI (AB 600 Plus) the amount of current being drawn by a motor at the instant that the accumulated value...
Replies
4
Views
2,309
Back
Top Bottom