Winklehoffen
Member
Hi all,
The gurus on this forum have helped me indirectly many times for which I am forever grateful, but now I feel the need to ask my own question.
Sorry to start a new 5/04 comms thread as I know there a plenty of them. Problem is I haven't found one that helps much with my problem.
I've come across a processor with a fault that won't reset and I'm unable to get online to it through the RS232 port to see what the problem is. Going online through the DH+ isn't really an option as I don't have all the required equipment and The Boss is very reluctant to stump up with cash for something we'll probably never use again (5/03s and 5/05s are our usual poison).
I have an offline copy of the code which shows the channel 0 setup:
Driver: DF1 full duplex
Source ID: 9
Baud: 9600
Parity: None
Stop Bits: 1
Control Line: No Handshaking
Error Detection: BCC
I have a 1747-CP3 cable and a laptop with a built in serial port (com1). The RS232 DF1 driver in RSLinx fails to autoconfig (check cables, etc...) so I manually entered the settings:
Baud: 9600
Station Number: 00
Parity: None
Error: BCC
Stop Bits: 1
Protocol: Full Duplex
The PLC is then refuses to show itself, which I find rather rude. I know there is no problem with the cable.
The customer suggested replacing the processor with a new one but I'm reluctant to do this because the fault may not be with the processor.
Any help is greatly appreciated and I shall sacrifice a kiwifruit to the deity of your choosing if you can help me sort this one out.
The gurus on this forum have helped me indirectly many times for which I am forever grateful, but now I feel the need to ask my own question.
Sorry to start a new 5/04 comms thread as I know there a plenty of them. Problem is I haven't found one that helps much with my problem.
I've come across a processor with a fault that won't reset and I'm unable to get online to it through the RS232 port to see what the problem is. Going online through the DH+ isn't really an option as I don't have all the required equipment and The Boss is very reluctant to stump up with cash for something we'll probably never use again (5/03s and 5/05s are our usual poison).
I have an offline copy of the code which shows the channel 0 setup:
Driver: DF1 full duplex
Source ID: 9
Baud: 9600
Parity: None
Stop Bits: 1
Control Line: No Handshaking
Error Detection: BCC
I have a 1747-CP3 cable and a laptop with a built in serial port (com1). The RS232 DF1 driver in RSLinx fails to autoconfig (check cables, etc...) so I manually entered the settings:
Baud: 9600
Station Number: 00
Parity: None
Error: BCC
Stop Bits: 1
Protocol: Full Duplex
The PLC is then refuses to show itself, which I find rather rude. I know there is no problem with the cable.
The customer suggested replacing the processor with a new one but I'm reluctant to do this because the fault may not be with the processor.
Any help is greatly appreciated and I shall sacrifice a kiwifruit to the deity of your choosing if you can help me sort this one out.