Trend for WinCC flexible

mr.bubu

Member
Join Date
Apr 2010
Location
Cheras
Posts
14
Can anybody know which settings can show for 24hours trending view at wincc flexi 2008..

Just now i can only show a few minute only if i set to a few hours then the trending will show quarter only..

If anybody know how to set it to show 24hours ???🤾

this my mail: [email protected]
 
I think you can have a maximum of 900 "points" on the x-axis. So you would have to select a sample rate of 24x3600/900 = 96 seconds.

Another solution would be to purchase an archives license. You can then setup archiving and a trendview that can scroll backwards in the archived data.
 
Can anybody know which settings can show for 24hours trending view at wincc flexi 2008..

Just now i can only show a few minute only if i set to a few hours then the trending will show quarter only..

If anybody know how to set it to show 24hours ???🤾

this my mail: [email protected]

Hi,


1. Set up a Data Log that that logs your inputs. This you can set in the Historical data\Data logs. Go for the storage location as "File-CSV" form.
If you are logging data's per minute, then in an hour 60 data's, and in a day 1440 data's. Hence set your "number of data records per log" as 1440.
Suppose if you are setting two tags in the same data log, the number of data records will be 2*1440 = 2880.



2. In communication\tags, select you required input tag. There will be an option for Data log and Logging cycle in the the "Tag" folder. select the Data log as the one you defined above and for cycle time, you can select as as you wish, 1sec, 2 sec, 5 sec, 10 min, etc.
(you can define your own cycle time in communication\cycle).


3. Now in the trends, define for the properties\x-axis value. In a day total 86400 sec are there. Hence define that value in x-axis.


4. Properties\Trend => select the trend type as "Log", and in source setting, select the log and the Tag entry from the drop down.
You can give a "Name".


Please note that if you had selected your Tag say "pressure" in the communication\tag folder for data logging, the logged file will be having a tag name as "pressure_0". Don't worry about this one.

and also while selecting from Trend Page, Properties\Trend. select the tag "pressure" only.
Only the logged data file will be having "_0" followed by the name.

hope this clears you.

rgds,
RBM
 
Last edited:

Similar Topics

WinCC flexible Trend View Can Show Maximum 8 Trends,What can be done if you want to show more than 8 trends in the same trendview. Can we use any...
Replies
6
Views
7,323
At the moment I’m working on a project to log a PID input (weight sensor) within a sample period of 20ms. Because Wincc cannot read value's...
Replies
4
Views
7,124
Hello everyone i want to use a trend in wincc flexible with two variables one for x axis and the second for y axis. i have found only with one...
Replies
1
Views
2,238
Dear all Can anybody help for I am using wincc flexible 2007 .In it I configure 20 numbers historical trends.Each trend has seperate tag and...
Replies
0
Views
3,691
Dear all I am using wincc 2007 to log the data. My client wants to see the historical data so that i have configured the trend view to show log...
Replies
1
Views
5,990
Back
Top Bottom