A-B PID instruction

tkhawkin

Member
Join Date
Jul 2010
Location
South Carolina
Posts
8
Hi, I am controling water temperture using an thermocouple card to a PID then to a analog output card. The problem I have is the valve ma signal is in the wrong direction. I am using a PLC5/40 processor. What is the best way to change this.
 
Last edited:
try changing the "Control Mode" or "Error" setting ...

E = SP - PV goes one way ...
E = PV - SP goes the other ...

and welcome to the forum ...

if you have other questions, please tell us what platform you're using ... not all Allen-Bradley PIDs are the same ...
 
Last edited:
Are you cooling or heating?

You can also try reversing your scaling so that 4mA = High_Process_Variable and 20mA = Low_Process_Variable.

Which analog card are you using?
 