You Americans are funny. I can't believe you don't need to be a certified journeyman to do electrical work in the States. Oh well, I guess since your accountants are more like fiction writers, it doesn't really matter......
 
I'm not claiming that all certified jouneymen are good, but they all somehow passed the coursework and exams. It's up to the state or province on how tough they want that to be......
 
Last edited:
Vetteboy said:
You Americans are funny. I can't believe you don't need to be a certified journeyman to do electrical work in the States. Oh well, I guess since your accountants are more like fiction writers, it doesn't really matter......

Americans have many monopolys but not on "incompetence". It is pretty evenly distributed around the world :)

No course can induce common sense
 
I'm not claiming that all certified jouneymen are good, but they all somehow passed the coursework and exams. It's up to the state or province on how tough they want that to be......

Very prestigious schools around the world graduate huge numbers of absolute idiots every year. We all know at least a handful of these individuals.
Until someone figures out a way to make that piece of paper do the thinking for someone, I'm not going to put too much stock in it.


By the way, I would stay away from running the 24 VAC with either 120 or 480 IF the 24 VAC is used for any signal sources. If it is just a supply for a contactor coil or a small drive, it's not a big deal. But you can and will induce noise into the 24 volt line if it is tied to a high impedence device. I usually think more in terms of signal versus driver than in terms of voltage level, up to a reasonable point and assuming the insulation is rated for the voltage.

Keith
 
Last edited:
I've seen folks run all kinds of things improperly in conduit together, and they break down into two categories:

1. "But we HAD to." (Two pipes/holes/sliprings are expensive)
2. "Prove we can't." (Hate salesmen and want us to suffer)

My favorite Category 1 was running encoder feedback in the same conduit as AC servomotor outputs.

But this question was about 24 VAC and 480 VAC together. I agree that good practice and the NEC says you should separate them with a barrier (when in tray), distance (when in cabinets), or 600 V insulation (when instances really, truly dictate).

I recently went through a situation where my customer ran 120 VAC signals into a controller input and they would "stick on" or give "false on" inputs. It turns out the 120VAC was run in the same conduit as 480 VAC motor leads, all the way from a local disconnect back to the MCC. The controller input was seeing about 70 VAC.... and it considered anything above 36 VAC to be "on". If you tied a solenoid or a contactor to this, the induced voltage would not have enough current accompanying it to affect anything. But a solid-state controller input is a lot more sensitive.

That was a combination of Category 1 and Category 2. It would have been much more expensive to run a separate conduit, and they'd succesfully run similar inputs to a different kind of controller input module without a problem.

We ended up redesigning our controller module to accomodate their installation !
 
My policy:

120 VAC with 24 VDC discrete I/O signals OK

480 VAC with 24 VDC discrete I/O signals to be avoided, VAC with 24 VDC relay or contactor control signals OK

Any AC with any analog signal (voltage or current) or communications wiring to be avoided

24 VDC discrete I/O or 24 VDC control with any analog signal (voltage or current) or communications wiring OK

You can (and I have) violate these guidelines and get away with it under some circimstances, but make sure you thoroughly test the signals and have a fallback position in case things don't work well.

(And as a side note, technically the insulation of the 24 VDC wire only has to be good enough to prevent breakdown and arcing of the 24 VDC to ground, since the 480 VAC wire insulation is already adequate to prevent breakdown and arcing to ground. You dont really need high insulation on the 24 VDC wires, although in the states most are insulated for 600 VAC anyway.)

Vetteboy: Passing journeymen's licensing exam doesn't mean an electrician is necessarily qualified to wire a light switch much less a control system, any more than passing the Professional Engineer's or HNC exams means someone is qualified to design an automation system. I agree that the US is behind the EU in many areas of control (120 VAC discrete I/O is still the norm over here, for example) but in defense of the US I have to say I've seen some damn fool things done both in Europe and in the US. Both systems typically have their relative strengths and weaknesses, and both have individual exceptions above and below the norm.
 
Just don't do it.......

The chances of something very bad happening are far to great.

Just another opinion.
 
quick question. Can i run 480vac 3phase in the same conduit as 24vac?

In the usa our electrical installation requirements are mandated by the NEC. This is strictly for the safegaurding of persons and properties from hazards arising from the use of electricity. In article 300.3 (c)(1) system wiring 600 volts and less allows for this installation . The answer is yes!

As pointed out above this is allowed but could cause problems in control systems using analog signals.

"Passing journeymen's licensing exam doesn't mean an electrician is necessarily qualified to wire a light switch much less a control system,"

Thats exactly what it means along with the installation of everything else covered by the code. A journeyman electrician must work under the direct supervision of a master electrican or he is not in compliance. The final installation must be inspected by the authority having jurisdiction. If all this is followed you will have a safe installation.
On control systems you need someone trained in controls. You don't go to an MD to have open heart surgery.

Vetteboy you absolutely do need an licensed electrician to install electrical in the USA but people don't allways do what they are supposed to, in order to save a buck. At least we have one accepted electrical code which clearly indicates what is acceptable (to qualified persons) for electrical installations which is more than can be said for the European community.
 
Last edited:
You Americans are funny. I can't believe you don't need to be a certified journeyman to do electrical work in the States. Oh well, I guess since your accountants are more like fiction writers, it doesn't really matter......

bawling
 
The other funny thing about you Americans is that you assume if I'm not American, I'm European. Well, my ancestors came from there over 100 years ago, but I live in that easily forgotten country north of you. I'm so embarrassed by my government that I don't fly that goofy liberal flag that we were forced to start using in 1965. We also have an electrical code here to save people's lives, and a real electrician knows that this is no joke. Non-electricians who see how easy it is to just "hook stuff up" are a hazard to everyone including you, so watch your step, Tim.
 
Last edited:

Similar Topics

Hello again..trying something on an existing poorly written program and just wanted to double check something system is an A-B MicroLogix 1200 In...
Replies
5
Views
163
Good morning! Let me start by saying, I am still learning about this type of HMI programming. I recently watched a video about recipes and how it...
Replies
0
Views
66
I have some logic that I have written within a 5380 series controller that tracks the time an event is started, while the event is running an RTO...
Replies
2
Views
89
I have an HMI 2711R - T4T Series B, and I want to know which PLCs, besides Micro 820, can communicate with it.
Replies
2
Views
80
HI i would like to know how to get a variable that will store the amount of times a program has been executed. The issue is I have 3 DBs for 1 FB...
Replies
2
Views
77
Back
Top Bottom