For a 2 wire connection we must use the connection like CH4, M+ and M-. But, what are U+ and I+ used for ?

regards,
Gerry
 
Hi Combo,
If you look at the Siemens manual, you can see that this module is not powered with 24VDC (you just have to connect all the M- terminals). If you want to connect a 2 wire 4-20 mA sensor for example, you need to connect to an external power supply. This module unlike the 6ES7331-7KF02-0AB0 is only passive.
 
2wire

But then 2wire connection between M+ and M- is not good, ... we need to use an external 24V...

L+ext to +sens and then ?

Hi Combo,
If you look at the Siemens manual, you can see that this module is not powered with 24VDC (you just have to connect all the M- terminals). If you want to connect a 2 wire 4-20 mA sensor for example, you need to connect to an external power supply. This module unlike the 6ES7331-7KF02-0AB0 is only passive.
 
Connection of a 2 wire sensor:
+ of sensor goes to +24V of the Power Supply.
- of sensor goes to I+ of the module channel you want.
M- of the module channel you want goes to 0V of the Power Supply.
 
ok

I understand, on page 299 I can see what you just said here. It's logic like this. Was confused, overlooked page 299...
Page 300 is for PT100 resistance measurement.

Thanks

Connection of a 2 wire sensor:
+ of sensor goes to +24V of the Power Supply.
- of sensor goes to I+ of the module channel you want.
M- of the module channel you want goes to 0V of the Power Supply.
 

Similar Topics

Hi all, i have a problem with the above card, my rack has two of them and the same issues! In Channel 0 and 1 on both cards i have 2 wire...
Replies
7
Views
1,890
Why when i connect all the 8ch of Analog Input(4-20mA) into the 6ES7 331-1KF02-0AB0 module the 4-20mA reading is not correct. example the input...
Replies
3
Views
2,937
I have a LM9030 program that is running on a IC693CPU331 that was installed in the mid 90's. How can I find out if this cpu can handle newer VP...
Replies
3
Views
1,258
Dear All, I wanna get the data from ind331 indicator(Mettler toledo) to SLC 5/05 CPU via Ethernet Ip using EEM instruction. The CPU=1747-L553...
Replies
2
Views
2,159
I've been fighting a problem with this 8 channel analog input card mentioned in the title. I believe it's something I'm doing in the wiring but...
Replies
3
Views
1,718
Back
Top Bottom