Analog module 8bits VS 12 or 14bits

Jeff23spl

Member
Join Date
Jan 2010
Location
Canada
Posts
860
i'm looking for a working solution and a 4in/2out module exist on my setup but it is a 8 bit only resolution. I usually use 12 or 14 bits that worked fine and i don't want to go into throubles.

IM not sure what it really mean in term of calculated resolution....can someone tell me how i can figure it out

is it: 2 exp 8 to give 256 meaning my range can only vary from 1 to 256 and meaning my values will move by step of 0.39% only ?
 
Jeff,
That's correct.

8-bit resolution gives you 0-255.
12-bit resolution gives you 0-4095.
14-bit resolution gives you 0-16383.
16-bit resolution gives you 0-65535.

The formula for percent change per step is:

1 / (max value) * 100 = % change

As your bit-count increases, your resolution increases; each increase/decrease in value represents a finer step in the value of your analog signal.

-rpoet
 
ok so i will spend a little more monney on buying my usual separate
8 Ai and Ao then using this 4ai/2ao 8 bit module....

I expect not enought resolution on this project....
 

Similar Topics

Good afternoon, I am currently working with an HMI/PLC LP-a070 and I require at least one analog output, but the PLC does not have one. I was...
Replies
5
Views
100
Why AMIo800 Analog input module's I/O LED is Lighting up Red? Checked module connections, 4-20ma wires etc but this light is continuously Lighting...
Replies
1
Views
111
In this sample programming, what does U4 mean? Any assistance would be greatly appreciated.
Replies
8
Views
273
I have run into a problem with my first time installing a 2080-OF2 module on a Micro820 and have a hunch that the module itself - brand new out of...
Replies
9
Views
930
Good morning Guys, PLC: micrologic 1500 LRP 24bwa c series soft: Rslogix 500 We are required to consider the weight of the product in such a way...
Replies
7
Views
1,391
Back