Hello!

I would like to know if I am rigth about repeater.
I have been reading the manual, but I have some doubts.
I put this picture. Is correct the conection.
The repeater have 2 segments A1 B1 -- A1 B1
A2 B2 -- A2 B2

But the second segments for what, I don´t understand
Is possible to use for another network

Thanks and my apologies for my knowledge

Reapeter.jpg
 
If you want to repeat between your 2 segments, your scetch is wrong. A1-B1 and A1'-B1' is the same segment, just duplicated terminals in case you don't want the repeater to be at end of the primary segment. The same is valid for A2-B2, A2'-B2'. The repeater function is also between upper and lower terminals. Note this: 1: The upper terminals are primary and the master should be connected here, to the left (A1-B1). 2: If there is only one cable coming in to the duplicated terminals, you must connect it to the leftmost terminal screws and put the terminal switch ON. If two cables are connected to a duplicate terminal - as on your scetch - the terminal switch must be OFF. 3: The switch in the middle will disconnect the lower terminals if switched OFF.

Kalle

PS! Congratulations with your soccer championship!
 
Last edited:
Thanks Kalle for your quicky answer! and the championship
So, If I understand well, I need connect IN to A1-B1 and OUT to A2-B2 and the switch on.
This is right.
 

Similar Topics

Hi, Any one please help me. At this time I at a site for commissioning. Here I got SIEMENS RS485 repeter ( 6ES7 972-0AA010OXA0) AND SIEMENS...
Replies
4
Views
10,374
Hi everyone, For that repeater, segment 1 has A1 & B1 and A1' & B1'. Which one is input? A1 & B1? Segment 2 both are output? Am i right? Pls...
Replies
1
Views
2,196
Hi, an overseas customer has a problem with a profibus network. There is one master. The network is segmented into two via a repeater (6ES7...
Replies
8
Views
8,352
Dear all. I know siemens repeater operating in layer 2 of OSI model, it check MPI and profibus frame. This repeater can not use with other...
Replies
0
Views
3,408
Dear all. We have a repeater of siemens( for Profibus, MPI). Can we use this repeater for other protocol, example Modus, DH485? Thanks.
Replies
1
Views
2,228
Back
Top Bottom