We have some AB CompactLogix PLCs running a coal/dirt separating plant. When an operator when to crank the plant this morning there was no comm between computer & PLC... complete comm loss. Upon further investigation it was found that the program had just disappeared out of the PLC... I saw where there was a known issue with a specific firmware version losing the program on an i/o fault/power cycle situation but wondering if anyone else has seen this problem? A copy of the program was downloaded back to the PLC and everything was fine... What say ye?
 
Does the PLC have a battery backup or use a compact flash card? If you had power loss and the battery was dead it would lose the program. Just a thought.

Tech4man www.tech4.com


Yes, good thought... unfortunately the night crew said there wasnt a power loss :confused: doesn't sound like we have all the pieces to the puzzle does it? lol
 
Yes, good thought... unfortunately the night crew said there wasnt a power loss :confused: doesn't sound like we have all the pieces to the puzzle does it? lol
Not just power loss but power spikes will whipe out the program or part of it from the PLC.
We had same issues with Compact Logix series controllers.
Surge protection/filtering will resolve most of your issues.
 
Also if it is running on a generator and the genny is shut down without the circuit breaker being switched off first, you can guarentee the program will be wiped.
Regards Alan
 
never underestimate the ability of an operator to screw things up.

over the weekend a stopped up float switch on a compressor turned into a "PLC" problem that required the operator to somehow clear the PLC memory. I always love that.
 

Similar Topics

Hello Dear users, I am writing about a problem that has been bothering me for a few days, i.e. I am trying to establish remote access to the Allen...
Replies
0
Views
87
Hello I need to message read the entire 16 channel raw analog inputs from a 1769-L33ER Compact Logic controller to another 1769-L33ER Compact...
Replies
8
Views
242
Hello, I want to monitor Wonderware historian's heartbeat and trigger a fault if Historian is not communicating /offline in PLC. Currently my...
Replies
0
Views
790
I would like to connect the compactlogic PLC to our network through the A2 port to enable cloud datalogging, but concerned about potential...
Replies
1
Views
1,508
Looking for AOI for Allen Bradley CompacLogix PAC for Statistical Process Control, SPC Functions like XBar, RBar,Average,etc: yakyak:
Replies
0
Views
1,276
Back
Top Bottom