I would like to ask, How to calculate the memory consumption of a given PLC? Specifically Simatic CPU-315-2 PN/DP? I can't find it in the help file. I just want to check if this cpu can handle 49 analog inputs and some digital input and output.

Your help is highly appreciated.
Thank you very much.
 
This should not be a problem for a recent version of the 315 CPU. Depending on which cards you use, u will probably have to install an expansion rack to.
The data sheet for the CPU shows you how big the address area is for the IO, but I would not go till the limit. The amount of memory you need is a bit based on experience. I always check the used memory and cycle time for every PLC I install. So after a while you get a feel for it. It is also very dependent on the complexity of the software.
 
@ Jobbe

Yes, I have setup a remote IO network using the bus interface module IM 153-1. All my remote IO will be communicating through profibus or MPI network. Thanks for the "tip" about the checking of memory consumption and cycle times. I will include that routine in my next projects, including this one.

@ Dchartier,

Thanks for the links you have provided. They were very helpful.

I would like to add, is there a formula on how to calculate the actual consumption? I saw someone do that but I can't figure out how he'd done that.

Again, thank you very much.
 
I would like to add, is there a formula on how to calculate the actual consumption? I saw someone do that but I can't figure out how he'd done that.
Memory consumption depends on how complex your code is.
For example you can use a start and a stop button to start a pump in 3 or 4 lines of code. You could control the same pump with extra control of a operator panel and a SCADA system on top, with interlocks, manual and automatic control etc. The second example will require more code and more memory. The same goes for analog signals. Do you use an analog input just to measure and visualize something or is it integrated in a complex cascading PID control?
Some companies develop their own spreadsheets that calculates the (estimated) required memory based on digital IO, analog IO, number of PID controls etc. This can be done if you use the same standard blocks every time. But it is still based on experience with previous projects.
Maybe Siemens has a tool on their site to help you with this, but I haven’t found it yet…
 
@ jobbe

Analog signals are for monitoring purposes only, so I think this will not consume much of the memory...

Thank you for your quick responses, I really appreciate them all.

Thank you.
 

Similar Topics

While selecting a PLC , what is thumb rule for program memory calculation?, Or How do we select memory size for PLC?
Replies
3
Views
1,726
Hello I am doing some research on plc memory allocation, including RAM, EEPROM, volatile and non-volatile variables etc. I would like to keep my...
Replies
5
Views
1,674
Is it possible to trend PLC memory usage in the historian? We are getting few faults on the compactlogix controllers. They are old running V17. I...
Replies
8
Views
2,050
Hello to everyone. I hope you are doing well. I have a KINCO PLC HP043-20DT. I'm communicating through free-protocol instructions XMT and RCV...
Replies
0
Views
1,239
I would like to create an AOI which throw me an alarm when cpu usage is more than 75%. Since GSV doesn not support this functionality I am...
Replies
7
Views
2,689
Back
Top Bottom