slc 5/04 w/uncommunicable dh485?

jaimeng6

Member
Join Date
Aug 2007
Location
alabama
Posts
52
Another comm. fault, I wouldn't of bothered you but I have exhausted all I've got! READ THE MANUAL SLC 500 HARDWARE STYLE TOO. PROCESSOR WAS ON DH485 NETWORK TRYING TO COMM. THRU ANOTHER NET AIC AND I FAULTED THE PROCESSOR SWAPPED IT OUT AND TOOK THIS ONE TO DEFAULT AS I HAVE OTHERS AND GOT IT BACK TO COMMS. MY QUESTION IS "IS IT POSSIBLE TO DAMAGE CHANNEL 0 SO IT WONT COMMM TO DH485 AND ONLY TO DF1?".
 
The slc 5/04 can do DH 485 if the port is configured for it.

All the net-aic module is doing is converting froma rs 232 wiring standard to a rs 485 wiring standard. The net aic baud rate and the channel buad rate must match.

Check the power to the aic module. You are powering it from a seperate suply correct? The manual says it can be powered from the chasis power supply but i really don't like to do that.

Set the available node number as low as you can this will help with speed.

I have seen some 5/04 with older firmware act up when set to dh 485 many times a reset to factory defaults is requied
 
Thanks for the advice Kid!
I had this 5/04 configured to dh485 until I tried to connect to it thru the network. you answered my question. I will have to keep defaulting over again and again.
 

Similar Topics

Howdy everyone, My company has a few machines running on SLC500 based PLC, and everytime it makes a part we count up on the counter which gets...
Replies
6
Views
152
Hello All! I am writing today because I cannot figure this out for the life of me. Another site I am affiliated with keeps having their slc 5/03s...
Replies
18
Views
382
I’m attempting to send a temperature from a SLC-5/02 to an EZiMarquee display. The vendor said to use a MSG instruction to send the data to the...
Replies
1
Views
111
Hello all. I have a few SLCs in my plant and of late we've seen a weird issue: The system will be running normally and then randomly the outputs...
Replies
2
Views
123
I am working on setting up a Prosoft Datalogger model PLX51-DLplus-232. This unit will be collecting data from a SLC 5/05 on the DB9 port set to...
Replies
3
Views
133
Back
Top Bottom