Iam beginner , so i want know how many i / o can be connected to cpu 317 - 2 - dp for example , and for interface module 153-2 i saw buttons called bus address ( how can i use it )is it for the modules that i connect it . Thanks alot
 
Hello tamerfahim;
1- here is a web page from the Siemens Industry Mall that will give you most of the information you need on the CPU 317-2DP (see the Product Information tab):
https://eb.automation.siemens.com/g...=gb&language=en&regionUrl=/uk#activetab=order&
For the same type of info on other CPUs, simply use the Search Box.

2- The IM 153-2 is an Interface Module for Profibus-DP. It allows S7-300 signal modules to be used as remote I/O over Profibus, acting as a Profibus slave.
The "buttons" you see are probably the address setting mechanism for the IM 153-2 (each DP slave must have a unique address on the bus that corresponds to the Profibus software configuration in Step 7).
Here is the same type of webpage in the Industry mall for the IM 153-2:
https://eb.automation.siemens.com/g...=gb&language=en&regionUrl=/uk#activetab=order&

Hope this helps,
Daniel Chartier
 

Similar Topics

merry christmas and happy new year i have a click c0-00dr-d and allen bradley 2711c-t3m. can the panelview talk to the click plc via modbus...
Replies
1
Views
214
Hello. There is a problem with Siemens S7 300. We got a replacement PLC but it does not run the program from the MMC. The new PLC is dated 2011...
Replies
3
Views
686
Hi Any one here please helpmein simulation of s7 300 plc program with factory io. how to connect. plcsim 5 doesnot have option of s7 300 ..:
Replies
2
Views
1,005
Hello, I have a bit of a situation, and I think I know the answer but this font of knowledge may prove something. I want to do the unthinkable...
Replies
6
Views
2,170
hello guys, I'm trying to establish a connection between Indusoft 8.0 & simatic Plcsim but I keep getting the following error: error...
Replies
3
Views
1,355
Back
Top Bottom