I am having an issue with a Automation Direct 110V AC Input Card(D2-16NA). This is connected to a Automation Direct D205 CPU. I am experiencing an Input Node failure. I am on my third Input card in the last month. This is on my safety circuit which contains 7 solid state switches. The backplane seems fine and I do not see any cracks in the switches. Has anyone come accross a similar problem?

Regards
 
Check the backplane receptacle where you plug in the input card. It has happened that a little piece of paper or lint gets jammed into one of the pin positions and intermittently blocks it. Those intermittent problems are a pain.

I once was in a computer troubleshooting class where the instructor deliberately stuck a piece of paper on one of the card connectors, and challenged the class to troubleshoot the PLC. Boy I will never forget that one.
 
Make sure that your voltage is not being spiked by the switching of the solid state switch or other parts of the circuit. The inputs on that card are rated for 130 Vac max anything above that and it pops.

Most siemens and ab modules have built in spike protection into the module. The AD modules do not.
 
I checked the backplane yesterday and everything looked fine. I am going to order a backup so I can change out the next time it happens.
 

Similar Topics

Hi, I have a ControlLogix system with 1756-IF16 analogue inputs. I can't scale the inputs at the card as there is a requirement to facilitate...
Replies
7
Views
158
I'm having trouble calming down 2 Tempo Sonics. I'm using Studio 5000 CompactLogix my Raw value is jumping around from 8575.0 to 8755.0 at a...
Replies
30
Views
1,104
I cannot add SLC500 analog input tag (I: 8.3) to EZSeries Touch Panel Editor (V 5.3). I used all the listed tag datatype but it all says "Invalid...
Replies
10
Views
250
Hi, I have questions. I have Analog Input that need to put into Ignition Designer. But I don't know how to put?
Replies
1
Views
111
Omron AD081-V1 Analog Input Card Offset & Gain Adjustment Entering Adjustment Mode 1. Set the input card in adjustment mode (Turn ON Dip SW No-1)...
Replies
0
Views
86
Back
Top Bottom