Panelview 1000 to slc 504

rstead

Member
Join Date
Dec 2009
Location
Edinburg
Posts
12
Trying to figure out a program to set up password protection for a "Start" button on a PV1000 screen. PV1000 communicating to a slc504. PW protection on PV1000 set up to secure screens only and not particular buttons.

Would like for when the operator press the "START" button on the PV a numeric screen comes up in which they enter their correct password. If password is correct with logic built into slc then the functions will start after correct password has been entered and acknowledged by plc.

Any sample password progamming out there between the slc504 and PV's?

Thanks,

Ron
 
Or create a numeric entry instaed of a start button. The PLC compares that to
a stored value in the PLC then gives a feed back to the HMI if it is correct or not.
 
Have done Mickey's example and made it work.

If it is a password you think your going to have to change and do not want to drag out a laptop each time you can create an expression for the limits so that when you change the password it changes the limits.
 

Similar Topics

Hello, I have been asked to update a really old system. It has a 1747-L542 (SLC 5/04 32KB) and a 2711-T10C8 (PANEL VIEW 1000). I have the...
Replies
9
Views
1,670
Hi, What configuration needs to be done in RSLINX ENTERPRISE RUNTIME in order that panelview plus 1000 to talk with SLC 5/03 ? I tried to copy...
Replies
6
Views
2,372
Hi, I can not make to communicate a SLC 5/04 with a Panelview Plus 1000. In Local Mode everything seems OK, but in Target ... I don't realize...
Replies
3
Views
3,226
We have a system with a Panelview Component 1000 and an SLC 5/03 on the floor. Does anyone know if the Component screen can be connected directly...
Replies
2
Views
2,753
Dear all, I have one Panelview 1000 HMI and one SLC 5/04 PLC. Both are Allen Bradley. Currently my Panelview 1000 HMI malfunctioned. So i need to...
Replies
5
Views
6,095
Back
Top Bottom