Dear Experts,
i have a S5 135U/155U cpu 928b


If I power up the system the Run led is off .QVZ & BASP led is on.

Digital Input led is ON but All digital output led is off

i connect step5 with cpu. upload my backup program (s5d). no problem to upload,but still same error.

Here is the photo--

CPU

http://i54.tinypic.com/i6e2ih.jpg


Digital input and output card.JPG

http://i53.tinypic.com/211sz2c.jpg

Error

http://i55.tinypic.com/k53eja.jpg

Error

http://i54.tinypic.com/2lng3dv.jpg

My Zennon SCADA is working fine.
Now, Please, tell me, is it a hardware fault??
and how could i find out the faulty card?


Thanks in Advance
ISteak
 
When you are in the Istack Screens, you hold down the shift key and press the right arrow button to go between each bit that is set. From the second screen, pressing the edit button will normally open the block in the editor with the cursor on the instruction following the one that caused the error.

You seem to have a PEU error which is likely to be a problem with a connection to an extension rack or a terminator on the extension rack comms cards.

Check all the connections and power supplies to the extension racks and then try a manual cold start of the processor.

Good luck

Nick
 
from my s5d program

it has 316 blocks

if i transfer all block to PLC Stop, BASP, QVZ Led is ON

and all output led is off but input led is on

if i delete OB13 & OB20 block from PLC then, Stop & QVZ led is off. Run & BASP LED is ON
(see attached s5d on zip)
i already try cold warm reset

now can you tell me how can i solve my problem??

which card is faulty digital input card or digital output card or...........??

i checked 24v in output it is all right but why there is no led on in digital output?

if 1 digital output card is faulty then every digital output card will stop working??

PLEASE TELL ME HOW CAN I SOLVE MY PROBLEM??


THANKS
ISTEAK
 
@isteak007
Your ISTACK has probably more to show if you press the continue key.

Kalle
Have you done this? - post screen shot.

You seem to have a PEU error which is likely to be a problem with a connection to an extension rack or a terminator on the extension rack comms cards.

Check all the connections and power supplies to the extension racks and then try a manual cold start of the processor.

Nick

Have you checked the extension racks power supplies?
Can you attach your program?
 
Yes i checked the extension rack power supplies....


Waiting for you reply.....
:confused:

From your screen pictures it shows an error occured in FB57.
From your program FB57 loads Perhipheral Byte ( L PY 0) however the byte accessed is determined by a "Pointer" in the line before the Load command (DO FW202)
Have you checked all the supplies to the cards - some cards have more than one supply to them?
 

Similar Topics

I am having a problem communicating my PLC with Drive via Modbus connection. I start by opening the port and there is no problem, but then when I...
Replies
6
Views
192
Hi everyone, Kind of new at this, so we recently upgraded our 1769-l32e to the newer 5069-L320erm, i converted the file over and Verify the...
Replies
8
Views
391
HELLO MY FRİENDS ı have problem. ı tought you can solved thıs problem for me. First of all When I checked all the cable connections of the...
Replies
0
Views
399
Hello, I am a beginner at Mitsubushi PLC programming. I am using a Q02CPU with some modules attached. I Am trying to move a servo through QD75MH1...
Replies
9
Views
367
Hi! I'm fairly new to PLCs, and a PLC I was swapping sensors for shows the error code 497 - 0x050000 on the top of the HMI when I powered it back...
Replies
6
Views
590
Back
Top Bottom