Thanks for replying Ron (I was hoping you would)...
I'm glad to hear that I should be setting the gains to "dependent" since I really thought "independent" was what I wanted...shows me that I shouldn't ALWAYS trust me gut feeling, haha.
This setup is to control the steam that heats water in a heat exchanger. Previously, they had the PID loop set up on an unconditional rung in the SLC, although I do not remember what they had the loop update time set at. In my new program, I put the PID loops in a periodic task that update once every second. I set the loop updates to 1 second as well. They had the Proportional at .5 and the Integral at .01 (no Derivative). So, those are the numbers I was planning on using when I installed the system (I don't install for another couple of weeks).
I have got the scaling setup as follows: I'm using a 1769-IF4 input card. I have the signal setup as "Scaled For PID" coming in. I believe, if I understand this right, that this will make it 0-16383. I have this as the Process Value to the PID loop. The output card I'm using is a 1769-OF4. From what I understand there is no "add-on profile" for this card in Logix5000, so I'll have to set it up as a generic card according to the manual. I haven't done that part yet, so I'm not sure about how to scale the output since it will not have a "configuration" tab on the menu.
I will see about sending you the program (although I'm not sure if I can due to company rules and such).