Panel Mate 1700 & CLX

Tawfiq

Member
Join Date
Sep 2010
Location
Saudi Arabia
Posts
3
Hellow Gents

I Have Planel Mate 1700 ( Cutler Hammer) and Control Logix contrlooer 1756-L61 (Rockwell).
Can I configure Panel mate to Write/Read To/From CLX data base? how?

Please advise.

Thanks in advance.
🔨
 
What network protocol is the PanelView using ?

In general, older devices can communicate with ControlLogix using the "Map PLC/SLC Messages" feature configured in RSLogix 5000 where each Data File Number (3, 7, 8, etc) is "mapped" to a ControlLogix INT[x] or REAL[x] array tag.

Only Binary, Integer, and Float(Real) data files may be used in this fashion.

My recollection of the PanelMate Power Series 1700 is that it is an older platform, about 10-15 years old. Is this correct, or is that still a product under current development by Cutler-Hammer ?
 
Thanks Ken, but I still need replacement for BTR and BTW instructinos, since Control logix software, haven't these two instructions.
How to Transfer / Recieve data to / from Panel mate?
Panel Mate will be configured as RIO rack at CLX via 1756-DHRIO scanner.
Discrete inputs and outputs could be programed at control logix software, but Data transmission still not clear

any Help

Regards.
 
Since you were using RIO communication, you must have the A/B Accelerat On card? It will also support the DH+ protocol. You simply must load the DH+ driver for it when you download your new configuration. This would be much simpler than RIO, I am sure. I have never used a PanelMate with a Logix CPU, so I don't know about native tag addressing, but I would expect that you can use the Map PLC/SLC addressing to get it done.
 

Similar Topics

Hi, I´m trying to download program to panel mate 1700, but these error messages are displayed. Any suggestions?. Thanks.
Replies
8
Views
6,066
Hello everyone, I have an Eaton IDT Panel Mate 1000 (P/N 92-00898-00) that I need to upload the program to my laptop so I can install it on a...
Replies
2
Views
1,469
I'm just discovered these vortex coolers from Automation Direct. I've never heard of them. They cost 1/10th of an A/C unit of the same BTU rating...
Replies
15
Views
8,972
Anyone know how to delete Allen Bradley drivers in a panel mate power series 3000
Replies
8
Views
2,199
Hi, I'm trying to convert an old HMI that uses a eaton panelmate and the software it uses is version 2.12. Does anyone know how to find the alarm...
Replies
6
Views
2,440
Back
Top Bottom