Problem with runing PLC

Iman

Member
Join Date
Jul 2010
Location
Tehran
Posts
172
Hi guys
I am working with a S5 Siemnce PLC CPU102. My problem is when I turn on the PLC, the red light of PLC turn on and when I change the state of the PLC from Stop to Run,it doesn't turn off and the green light turn on just for a moment. I can connect to the PLC and load or store program. I have changed it with a new one but the problem still remains. Can anybody guide me where the problem is? also does anybody knows abot this tag that I found it on the PLC "E-Stand 03", tis tag in the new PLC was "E-Stand 04", what's the difference between these two?
 
Not sure if it's the same for 102 but on the 95u a new plc that has not been programmed will not go into run.
The procedure is to remove the battery, power up switch from stop to run a few times then when the plc run light comes on put it back to stop, insert battery while still powered up then switch to run, you can then power down but leave the battery in (if my memory serves me right this is to generate DB1 the processor config db.
This assumes the old processor is duff & the new one is ok.
 
Solve it

Thank you guys for your respond.
I found the problem and solved it. The problem was in the slot bus.First rack and second rack wasn't tightly fix on their slots :D
 

Similar Topics

Hi, I have had problem with upgrading some projects from v16 to v18. I tried it on 3 diffrent computers. I want to post this so that anyone that...
Replies
3
Views
116
Hi, I am having a challenge installing a new drive ACS355-03E-44A0-4 as it keeps on displaying Fault code F00018 even when the load is not...
Replies
3
Views
129
I have an issue on my vessel, we have water tight door system created in China, company is no longer operating. We have 7 doors each with their...
Replies
3
Views
114
Hi all. Simple as simple can be, I don't understand what's happening. I'm toggling he OSR on, GX_LUB_PUMP1_LEAD should switch. It doesn't. The...
Replies
27
Views
646
Hi; In a cabinet of a machine, a Fatek PLC with an Ethernet communication card is working. In the same cabinet, there is a 1 kW inverter. When...
Replies
16
Views
492
Back
Top Bottom