Powerflex 40 with ethernet option

HAVERI

Member
Join Date
Oct 2010
Location
HAVERI
Posts
1
MY INTENTION IS TO CONTROL POWERFLEX 40 ON ETHERNET. DO I NEED TO CHANGE ANY WIRING ON THE CONTROL TERMINALS ON THE DRIVE OR LEAVE THEM AT FACTORY DEFAULT (i.e. leave the jumper on terminals 1 & 11). I AM GOING TO REMOVE THE HIGH VOLTAGE POWER FROM THE DRIVE WHEN EMERGENCY STOP IS ACTIVATED.
 
MY INTENTION IS TO CONTROL POWERFLEX 40 ON ETHERNET. DO I NEED TO CHANGE ANY WIRING ON THE CONTROL TERMINALS ON THE DRIVE OR LEAVE THEM AT FACTORY DEFAULT (i.e. leave the jumper on terminals 1 & 11). I AM GOING TO REMOVE THE HIGH VOLTAGE POWER FROM THE DRIVE WHEN EMERGENCY STOP IS ACTIVATED.

No, but you will have to change some of the PF40 Parameters to tell it to be controlled by the 22-COMM-E.

22-COMM-E Manual is 22COMM-UM004B-EN-P

PF40 Manual is 22B-UM001G-EN-E

You can Download them at the AB Literature Library for free.

http://literature.rockwellautomation.com/idc/groups/public/documents/webassets/browse_category.hcst

Stu....
 

Similar Topics

So I have a sort of unique situation where I'm wanting to run a PF755 from the IO and over ethernet. Of course, this comes with it's own set of...
Replies
9
Views
252
Hi guys! We have a big project at work where we are migrating from 1305, 1336, 160, 70, and 40 drives to identical PowerFlex 525 models. Most...
Replies
3
Views
882
Hello, I have an existing application that has a Powerflex 700 with a 20-COMM-E adapter controlled by a Micrologix 1100 via Ethernet. The setup...
Replies
6
Views
1,192
I have a contractor at my water plant installing 3 brand new Powerflex 7000 VFD's for my High Service pumps. I would like to control these via...
Replies
6
Views
996
Hi All, I am working on testing a project with a Powerflex 525, final project will be a 755, and I am trying to reset the Elapsed kWh meter over...
Replies
3
Views
588
Back
Top Bottom