I have a tank where they (other company) placed a 0-6 Bar Pressure transmitter. The Tank can have 20000 liters of butter max. There is a tracing around the tank for warming up the tank so that the butter stays a little liquid. The density of butter is 0,86 kg/dm3.
The Pressure transmitter gives a signal from 4 to 20mA to an S7 PLC.
So 4mA = 0Bar
And 20mA = 6 Bar
When they delivered 5000 liters butter, I had a signal of 4.741mA
So this gives us:
Range = 20mA - 4mA offset = 16mA
Signal = 4,741mA - offset = 0,741mA
(0,741mA * 16mA) / 6 bar = 0,278Bar, or 278mBar
Because of the range 0-6 Bar we have problems for showing the right volume in the Tank.
When they have 1000 liters remaining in the tank for example, then 0,741mA / 5 = 0,1482 mA + offset = 4,1482mA.
So I think they should place a pressure transmitter with a lower rangen, like 0-1 Bar for example. Or measuring ultrasonic from upstairs. De density of butter in combination with the transmitter 0-6 Bars is giving probs right now. When they should see 3000 liters, this can also be 1000 liters or 4500 liters...
Any suggestions on what I can do ?
Is the Pressure transmitter usable ?
Or is the fault more a problem because of the tank not being lineair (filled and allmost empty on a certain curve) ?
Please help,
Thanks in forward,
Regards,
G
The Pressure transmitter gives a signal from 4 to 20mA to an S7 PLC.
So 4mA = 0Bar
And 20mA = 6 Bar
When they delivered 5000 liters butter, I had a signal of 4.741mA
So this gives us:
Range = 20mA - 4mA offset = 16mA
Signal = 4,741mA - offset = 0,741mA
(0,741mA * 16mA) / 6 bar = 0,278Bar, or 278mBar
Because of the range 0-6 Bar we have problems for showing the right volume in the Tank.
When they have 1000 liters remaining in the tank for example, then 0,741mA / 5 = 0,1482 mA + offset = 4,1482mA.
So I think they should place a pressure transmitter with a lower rangen, like 0-1 Bar for example. Or measuring ultrasonic from upstairs. De density of butter in combination with the transmitter 0-6 Bars is giving probs right now. When they should see 3000 liters, this can also be 1000 liters or 4500 liters...
Any suggestions on what I can do ?
Is the Pressure transmitter usable ?
Or is the fault more a problem because of the tank not being lineair (filled and allmost empty on a certain curve) ?
Please help,
Thanks in forward,
Regards,
G