Hey everybody.

I have a problem with the analog input as I want to convert. for this purpose I use a FC105 scale converter. I come with a 4-20mA signal. Where 4mA is 0 and 20mA is 100 And this should show on a touch screen. But the output of FC105 need? Did not really it works. On my display I have a bar meter. But here I just get a yellow arrow that shows up. Just like on the outside range. I am attaching just my scale block.

Anders Larsen

FC105scale.jpg
 
It effects the output, I either place an always on or always off flag that I create there.

Bi-polar means +/- signal.

If that input is on and the signal is not bi-polar it will read wrong, if the input changes state the output will.

highlight FC105 and press F1 for info.
 
I come with a 4-20mA signal. Where 4mA is 0 and 20mA is 100
But you wrote there 1 Not 100

Try to Write 100.0 to HI_LIM
100.0 = 1.000000e+002
Also check these:

Try to put Always 0 to Bipolar. IF OK
did u download FC105 to plc? IF YES
Do you see values in PIW276? IF YES
Did you use MD40 at somewhere else in your plc program? or MW40 or M40.0? IF NO

THEN You must see some values in MD40 ( changes from 0 to 100 )
 
Hey

I can see the value in md40 moves between 0-100 depending on the 4-20mA.
But how few I saw this value read on my screen. I want that value displayed in a bar meter. on a mp277 10 "display from Siemens.
 
unfortunately I did not install wincc flexible.
but you must just creat tag floating point address MD40
and u must click properties of bar and write your tag name to there.

you can read wincc flexible manual.
 
Hey

I can see the value in md40 moves between 0-100 depending on the 4-20mA.
But how few I saw this value read on my screen. I want that value displayed in a bar meter. on a mp277 10 "display from Siemens.

Hello alarsen

From Simple Objects Menu on the right choose "Bar". In the properties menu below select your process varaible "x" and arrange other properties of the bar. Since your scale is 0-100 you dont neede to change max and min values. Hope this helps.
 

Similar Topics

So, we have one servovalve that is very critical to machine operation and idea is (or was) to detect if valve gets disconnected from analog output...
Replies
11
Views
2,871
Hello, We monitor the temperature of a pipe via a 4-20mA temperature transducer. This goes into DB135(Read Analog Inputs). The issue I have is the...
Replies
0
Views
624
I am setting up a new system and have an s7 1214 plc with an sm1231 4x AI (6ES71231-4HD32-0XB0). It is configured for 0-10v and has no faults in...
Replies
5
Views
1,130
Hey guys! I have come across an unique issue. Hoping that I can find some solution here. I want to replace an existing S7-1214 DC/DC/DC plc with...
Replies
15
Views
4,646
When using Turck BL20 analog and Siemens S7 can someone tell me if the scaling in S7 is still 0-27648 (for 0-10vdc/4-20ma) or is it something...
Replies
3
Views
1,836
Back
Top Bottom