Current Sensor

winch

Member
Join Date
Jul 2010
Location
california
Posts
14
Is there a current sensor available that can measure a three phase 480 Vac with a rating of 18 A? I would like to do an automated monitoring system for the current draw for our heating elements. i have more than 180 elements to monitor. Is there something available that i can sort of networked to a single controller and be able to monitor all current draw for each elements?
 
Using current transformer is bad idea?
You can convert secondery of current transformer (generally AC 5A) to 4-20mA with weidmüller convertors.Then you can send this information to your controller.
 
There are current transformers that convert directly to 4-20 mA. We use some from Carlo Gavazzi.
You should install a compact distributed i/o of your choice (Profibus, Devicenet, Can, whatever) to collect all the 4-20mA signals.
What controller or fieldbus do you have in mind ?
 
ABB Current Monitoring Relay

If you are monitoring electric heat, the load amperage draw will be consistent.

I assume you are looking for a simple pass/fail (heater burnout detection) digital relay, as opposed to actual current transducer, which would provide anaolg signal proportional to amperage draw.

Here is a link to ABB CM-LWN motor load monitors.

http://www.abb.com/product/seitp329...fe00302388.aspx?productLanguage=us&country=US
 

Similar Topics

Hi, I've got experience with siemens s7 plcs, rockwell and schneider plcs but having trouble with this generator controller (InteliGen 200 Comap)...
Replies
1
Views
1,259
Dear Experts, Is it allowed to use 4 wire sensor 4-20 ma (external power loop) with control logix analog card ( 1756-IF16 )with a single...
Replies
6
Views
3,034
I am doing a project to detect power spikes. I am using current sensor ACS712. I am using the analogue channel FX2N-4AD of the Mitsubishi PLC. The...
Replies
5
Views
3,121
Utah Integrator at wits end and about to comment ritual suicide with my multimeter probes. Please help a brother out. Culinary water tank at the...
Replies
15
Views
6,969
I need a little help locating a CURRENT TRANSFORMER or CURRENT TRANSDUCER with a hole of about 7/8 or larger but I need like a 0-1 amp range...
Replies
11
Views
4,556
Back
Top Bottom