We are looking at an application with 10x VSD's, that have Modbus RTU by default. We can also easily add an E/IP card to the VSD.

At this stage we are angling towards a ML1400 & Modbus Serial, but I was just reading a thread abuot the L23E. What would be the option that others would look at for this type of application? The ML & Serial option is far cheaper, but E/IP is so much easier to configure, maintain & support going forward.

I'm assuming the L23E can have E/IP devices as IO etc?
 
Hi,

You will not have the best update times with Modbus. My rule of thumb is to have max 8 slaves on a Modbus RTU network at 19600Bits/s using a few coomand/slave. So, if you have any concerns about update times, I suggest to go with EtherNet/IP.

Just my 2 cents

Patrick L
 

Similar Topics

I have a PH meter that I am trying to bring its data into 1756-L81. I have downloaded the Rockwell MODBUS AOI kit, but I am not sure if I need to...
Replies
5
Views
148
Hi all. Customer wants analog faceplates really bad, even if we explained that it doesn't make much sense in his process. What he wants to see...
Replies
5
Views
110
Hello, recently I saw a graphic from any Rockwell App, I cant identify which one is. Attached a SS. Its used to see dashboard from datapoints and...
Replies
2
Views
127
I'm working with a project that contains some routines in ST but mostly in ladder. Am I correct in assuming this 'rung': DB1001DO._01AV55_OPEN :=...
Replies
4
Views
113
I noticed in Rockwell AOIs, they add a BOOL Output parameter at the end of the "Parameters" list of each AOI that carries the same name as the...
Replies
1
Views
75
Back
Top Bottom