CLX BTR MSG error

eazyu2000

Member
Join Date
Dec 2006
Location
Orapa
Posts
3
Hi guys please help me with this one. I am doing PLC5 migration to CLX system, im using a 1756-DHRIO to scan remote IO racks with (1747-ASB). Some of Analog IO scans bring up the following error on BTR MSG Block - "Error code: 16#0001 Extended error 16#0076_0113 Error Text: Connection failure". The communication between the remote racks and DHRIO is healthy and does not have faults. I am using BTR MSG to read analogs and have arranged them in groups to try to eliminate the error but to no vain đź“š
 
How do you have the block transfers configured?
You need to directly read the module, not the rack.
In the configuration, you set the right channel for the DHRIO module, the rack address of the ASB is set in OCTAL... Check the module DIP switches. The 'Group' should be set to the slot the analog card is in, 'Slot' should be 0. And, of course, you should be reading the correct number of elements.
 
I have configured MSG BTR block to read each slot which has 4 channels. My problem here is that some slots bring up errors on the MSG block. I have tried looking for the meaning Extended error code: 16#0076_0113 but can't find any.
i have attached file of configuration
 
Welcome to the Forum !

Ideally, open up a new thread and reference this one or simply lay out your issue separately.

Unless your system was exactly the same (1756-DHRIO with 1747-ASB and multiple analog modules) it's likely the problems and solutions are different.

On that old thread it looks like we never got to the point of even figuring out if it was an addressing problem, a hardware problem, or a capacity/buffer problem.
 

Similar Topics

Hi guys please help me with this one. I am doing PLC5 migration to CLX system, im using a 1756-DHRIO to scan remote IO racks with (1747-ASB). Some...
Replies
1
Views
3,086
Controller: 1756-L84E v.35 Prosoft MVI56E-MNETC for ModbusTCP/IP I'm having an issue with some of my write commands. The write command that...
Replies
0
Views
171
I have several Avery scale units and they are configured as Generic Ethernet modules, and I am actually reading the data fine for the weight...
Replies
2
Views
358
What's the best way to move a tag value from the panelview+7 to the clx plc. We display amps from a power meter on the panelview screen, read in...
Replies
1
Views
382
I'm running into an issue migrating a PLC-5 using the newer Logix Designer Export when opening a saved .ACD from RSLogix-5. It has multiple RIO...
Replies
2
Views
598
Back
Top Bottom