I'm trying to simply change a timer preset value from 100 to 500 (x .01 sec) using RSLogix 500. It allows me to highlight the value and type in the new value, but when I hit enter, it reverts back to the original '100' value.

I've tried making this change on the ladder code screen as well as the 'Timers' table, with the same result.

For troubleshooting purposes, I proved that I could successfully change several other timers, but this particular one doesn't permit a change.

Any suggestions? Maybe I should just re-write the line of code.

Thanks in advance,
Tom
 
Problem solved. Elsewhere in the code, I have a MOVE statement that moves the timer preset value to the line that I was trying to change (depending on a switch position). That's why it wasn't accepting my manual change.

Thanks for your help This help forum is great.
-Tom
 
Problem solved. Elsewhere in the code, I have a MOVE statement that moves the timer preset value to the line that I was trying to change (depending on a switch position). That's why it wasn't accepting my manual change.

Thanks for your help This help forum is great.
-Tom

To be pedantic and precise, your RSLogix500 software was making the change to 500, so your highlighted statement above isn't technically correct.

The value you entered was being set into the timer preset register, but your code at some point in time later was re-writing it back with your MOV instruction. So there was a finite time when the preset value was at 500.

The reason I make this distinction, to give warning, that there might, possibly, be code elsewhere that inspects this preset value, perhaps (for example) to enable another function if the preset is greater than 250..... Your manual input of that higher value may "trigger" unwanted actions.

The warning is issued with regard to safety, personnel and machine or process "damage" - it is not wise to go poking values into any data-table locations without a full understanding of the implications, and an assessment of whether the changing of a value will cause problems should be made.

Your Cross-Reference facility will be your friend here - you can use it see where any references to that data-table value is made in the program.

This is especially true if you, personally, didn't write the whole program, and even if you did, you may have forgotten that you used such-and-such a value to do something else.
 

Similar Topics

i cannot uninstall RSlogix 500 v9 from laptop. in control panel, remove window stays freezing for days. i tried to reinstall it to get the new...
Replies
7
Views
3,537
This error is inconsistent. Most of the time I try to open RSLogix500 it gives me the error along the lines of "Server busy, action cannot be...
Replies
7
Views
19,110
Hi Everyone, I am not proficient in RSLogix 500 so I have a question regarding the evaluation of N7:0 data as an input. So as I understand in...
Replies
1
Views
79
I have a little bit of experience with Allen-Bradley. I have a Micrologix 1500 (RSLogix 500) and a PanelView Plus 7 (FactoryTalk View Studio ME)...
Replies
3
Views
159
buen dia. tengo una falla al pasar los tags de mi plc SLC 5 0/4 a mi panel me aparece un error Problem writing value " " to item <tag name>...
Replies
1
Views
81
Back
Top Bottom