Hello,
I have been pulling my hair out for 3 days now. PLEASE HELP
I had a PowerFlex 70 VFD go down and had it repaired. I installed the VFD back into the Mcc and I powered it up. I was able to program the Node Address back in as #3 and get it back online with Devicenet. I then loaded the parameters via DeviceNet. After dowloading the EDS File. Everything is going well so far. I then pulled up RSVIEW32 to see if everything looked good on the screen. I have a HOA on the screen. So I went out and double checked my switch on the MCC it was in auto. I then pulled out my meter to verify that I had a closed circuit on my thermal leads, I did. I then proceeded to check my switch to verify that it is making proper contacts (open and closed circuits) for the drive to see, It was. I jumpered 7 and 8 to rule out the thermal protection of the motor. So I am stuck trying to figure out why the VFD works fine in Manual mode at the MCC and I can see the Feedback Hertz on RSView32 even though its not the right amount of Hertz.
I think something was changed and I am unable to find it in RSLogix5000. If you guys could help me out it would be greatly appreciated.
A person that is no longer with us at the plant had pulled the drive and put another in place to get the plant up and going. The problem was this drive was only temporary because it was used in another part of the plant which was down at the time. I have since pulled that. VFD and put it back in its original place and it is up and running just fine.
Thank you for your time
I have been pulling my hair out for 3 days now. PLEASE HELP
I had a PowerFlex 70 VFD go down and had it repaired. I installed the VFD back into the Mcc and I powered it up. I was able to program the Node Address back in as #3 and get it back online with Devicenet. I then loaded the parameters via DeviceNet. After dowloading the EDS File. Everything is going well so far. I then pulled up RSVIEW32 to see if everything looked good on the screen. I have a HOA on the screen. So I went out and double checked my switch on the MCC it was in auto. I then pulled out my meter to verify that I had a closed circuit on my thermal leads, I did. I then proceeded to check my switch to verify that it is making proper contacts (open and closed circuits) for the drive to see, It was. I jumpered 7 and 8 to rule out the thermal protection of the motor. So I am stuck trying to figure out why the VFD works fine in Manual mode at the MCC and I can see the Feedback Hertz on RSView32 even though its not the right amount of Hertz.
I think something was changed and I am unable to find it in RSLogix5000. If you guys could help me out it would be greatly appreciated.
A person that is no longer with us at the plant had pulled the drive and put another in place to get the plant up and going. The problem was this drive was only temporary because it was used in another part of the plant which was down at the time. I have since pulled that. VFD and put it back in its original place and it is up and running just fine.
Thank you for your time