I am having some poblems with a pH transmitter. MAybe someone here can help.

We have a pH probe mounted in a drinking water pipe with flowing water. It is a flat face probe designed to be in a flow.

The pH of the water in the pipe is about 7.5.

Al of the sudden the value displayed on the transmitter starts to drop slowly following a straight line. Maybe from 7.5 to 4.5 in two hours. We have a handheld meter that verifies that the actual value is around 7.5 Both the display and the 4-20ma signal drops.

The cable to the probe is screened.

The transmitter is mounted in front of a cabinet. The cabinet contains a small PLC, display, powersupplies, some small relays. It is supplied by 230V AC 50Hz. No threephase or motor control.


Any ideas? EMC? If it was electrical
disturbance I would say that it would be more noise than a decreasing signal.
 
Hello,

I am having some poblems with a pH transmitter. MAybe someone here can help.

We have a pH probe mounted in a drinking water pipe with flowing water. It is a flat face probe designed to be in a flow.

The pH of the water in the pipe is about 7.5.

Al of the sudden the value displayed on the transmitter starts to drop slowly following a straight line. Maybe from 7.5 to 4.5 in two hours. We have a handheld meter that verifies that the actual value is around 7.5 Both the display and the 4-20ma signal drops.

The cable to the probe is screened.

The transmitter is mounted in front of a cabinet. The cabinet contains a small PLC, display, powersupplies, some small relays. It is supplied by 230V AC 50Hz. No threephase or motor control.


Any ideas? EMC? If it was electrical
disturbance I would say that it would be more noise than a decreasing signal.

Make and Model of the PH Probe?

Stu.....
 
pH is (was?) commonly measured using conductivity. IF the conductivity of water increased suddenly then that may affect pH reading.

One possible cause is sudden flow in water mains ie fire department fighting a fire. High flow in mains shakes loose all the rust and sediment in pipes.

Did you check probe in a standard pH solution? That is the first thing I would do.

Dan Bentler
 
I have seen a similar situation.

My cure was to make sure I had an earth near or around the probe but not touching the probe itself .

My feeling was that the material of the pipe and near a bend was allowing a skin charge to develop, which was affecting the PH probe and causing the creepage.
I never resolved the issue I just lived with the earth till we shifted the probe when we installed new PH controls
 
I have seen a similar situation.

My cure was to make sure I had an earth near or around the probe but not touching the probe itself .


Tried this today I connected a wire from the earth in the cabinet to the pipe. My problem was that today I could not force the problem to show at all. Hate this type of problemso_O
 
If my problem is not due to grounding but instead of interference. Could a ferrite core like the one used on the cord from a laptop powersupply be a solution??
 
I will throw another suggestion

If in the cable used from the PH probe to the Meter you have wire cores that are not used tie them down to earth at one end as they possibly could start picking up a capacitive charge that might affect the signal

My feeling is that I would not expect the ferrite to make a difference unless there was some high frequency noise source nearby
 
After the pH Probe(1m) on the pipe some water is diverted to go in to a electrolyze equipment(2 meters hose). The flow in the main pipe can be 10-100 lpm and less than a liter per minute is diverted.

Can electrical charge from this equipment affect the conductivity in the water and affect the pH probes reading.
 
>Can the process/piping affect a pH reading?

Yes. The pH probe's electronics are measuring picoamps of current. The circuit can be affected by external potentials in its installed environment.

A grab sample in a glass beaker on a lab bench is well isolated electrically. A process might or might not be.

There are some installations where I could find a solution. Once, I discovered the AC powered analyzer wad not earth grounded. Another time I removed the earth ground ( the 24Vdc power supply had its negative side earth grounded.

Before you chase stray voltage or grounding issues, have you calibrated the probe to check its response?

Is the process changing temperature over the time that you see this downward drift in pH? (is the temp comp circuit functional?)
 
>Can the process/piping affect a pH reading?

Before you chase stray voltage or grounding issues, have you calibrated the probe to check its response?

Is the process changing temperature over the time that you see this downward drift in pH? (is the temp comp circuit functional?)

I said it before and I say it again
HAVE YOU CHECKED THE PROBE IN A KNOWN SOLUTION?
That is two of us suggesting this.

Uhh have you even checked the pH in your system?

Dan Bentler
 
I said it before and I say it again
HAVE YOU CHECKED THE PROBE IN A KNOWN SOLUTION?
That is two of us suggesting this.

Uhh have you even checked the pH in your system?

Dan Bentler

Sorry that I did not reply to above but yes of course I did check in a known buffer solution.


However today I resolved the problem. The Display/Transmitter had a PT100 input for temperature compensation. The probe that is used has no PT100 and the temperature is quite steady.

When there was no PT100 connected the terminals for the PT100 where supposed to be connected together. Did so and all of the sudden it worked.o_O
 
When there was no PT100 connected the terminals for the PT100 where supposed to be connected together. Did so and all of the sudden it worked.o_O
Are you sure you are suppose to just connect them together? Usually there will be a chart or formula to figure out what size resistor to put across the terminals for a given water temperature. If it requires a resistor you will not get a linear value with a jumper
 

Similar Topics

Does anyone have experience wiring this type of analog pressure transmitter up? It's 4 wires. 3 blacks and 1 green which I assume is earth...
Replies
9
Views
264
I need to protect some pressure transmitters from hot (120°C) oil. Does anyone have a favorite transmitter cooling element/standoff they use...
Replies
4
Views
166
Hi ,when i check the 4-20 ma output from flowtransmitter with multimeter ,it can shows 4 ma , but when i check with process meter it only shows...
Replies
1
Views
160
How fail safe mode in level transmitter works? customer requesting for fail safe mode when the transmitter got any issue or power loss on the...
Replies
4
Views
979
Hi - I have an application where there is an option to use a PID loop embedded in the Transmitter to directly control (via 4-20mA output from the...
Replies
4
Views
1,069
Back
Top Bottom