Hi, I have two questions, and I hope I can get some help plz.

First: At work we have one system with 3 PLCs S7-400. They are using RAM to store the program. I was wondering, if I requested for EEPROM instead of RAM, will that EEPROM contain even the configurations (Like IP address, etc..) (Thus in case of PLC failure any technician can just replace the PLC and install the backup eeprom. ??? (Or still requires configurations using Symatic S7 ??

Second: If I changed the way Profibus is connecting devices, does it require any changes on the PLC Program side? (Like we have PILZ-E-Stop PLC- in the middle of the Profibus network, and I we were thinking to have it on a seperate line (thus any work on the segment, won't affect the entire system.

Thank in advance.
 
If you change from a ram card to eeprom the system data will
Be retained Make sure you still keep the battery so that a power cycle will keep your setpoints etc..

You can move a device to any location on your network, even through a repeater.
I hope this is clear and helps
 

Similar Topics

Kindly, we are trying to go online on an S7-300 plc, with profibus communication, using a CP5711 adapter. But when we open the Ladder and press...
Replies
0
Views
778
Dear Sir, I have a healthy profibus communication between SIEMENS PLC S7 400 and Allen Bradley drive PF700 using 20-comm-p profibus dp module...
Replies
3
Views
2,809
Dear all, In the past I have used DP/PA Links with Siemens PLCs. As both the Link and the PLC was from the same vendor, ther was no trouble...
Replies
2
Views
3,088
Greetings Can the Profibus network ، Schneider Premium PLC with TSXPBY100 Module was selected as Slave? I'm going SIEMENS PLC (S7-400) as master...
Replies
3
Views
2,350
In plant we use Siemens S7 PLC CPU 319F-3 PN/DP with profibus connected to remote I/Os. Profibus network have profibus nodes. We are getting...
Replies
4
Views
6,991
Back
Top Bottom