I have an ethernet system running through plant server. I am able to access wirless the varrious devices in the plant with the exception of the DIGI ONE IAP modules. they show up in linx classic 2.56 as a yellow ? but say Digi One IAP. is there
somthing I need from AB or Digi to resolve this. Thanks
 
I am using Linx Classic 2.56, I have not downloaded anything from Digi
I will try to research their site for update.
 
Once the proper EDS files are installed, the digi module should become transparent and the connected PLC icon will appear if you're using the ethernet devices driver in RSLinx.

Using that driver, you will only see the digi icon when the connected PLC is not communicating. If you use the Ethernet/IP driver in RSLinx, the digi icon will always appear.
 

Similar Topics

Hello, I am using a Digi One IAP and CompactLogix PLC to read some Modbus registers from a Kohler Generator. Things are working, except when I...
Replies
1
Views
1,231
Sorry, have to vent here. I've used a number of Digi products over the years with success. We recently installed a number of the Digi ONE IAP...
Replies
27
Views
8,006
Hi I am trying to set up a serial to ethernet Digi One IAP so that data can be read in Studio 5000. issue I have is finally got RSLINX to accept...
Replies
1
Views
2,005
Has anyone had similar issue? I have a digi one iap modbus tcp converter polling abs RTD data from pump controllers. I am new to the issue, but...
Replies
2
Views
1,440
Title says most of it. I have a thermon tcm2 heat Trace controller that is modbus rtu. It's hooked to a digione iap to which I have hooked to my...
Replies
4
Views
2,378
Back
Top Bottom