Induced Voltage Activating Input

bluenoser337

Member
Join Date
Apr 2003
Location
Nova Scotia
Posts
391
I have a 24v DC input that is coming on from about 9 volts of induced voltage. I believe I can connect a resistor between the input and 0v to "pull down" this voltage to an acceptable level. Not sure of what value and wattage to use. Any help appreciated! Thanks!
 
Hi Bob...I knew somebody would say that. The machine was installed with AC and DC in the same cable. This should be fixed, for sure. For now, the machine needs to run.
 
You just need to make sure the resistor won't overheat with 24 Volts on full time or load down the device it originates from
e.g. 1/4 Watt
0.25/24 = 0.01 mA
24/0.01 = 2400 Ohms (minimum)
Assuming your cable is < 100 meters I think you will find a much larger resistor will do the trick e.g. 10K
Please let us know the final solution.
I assume your cable is not one with shielded pairs.
Roy
 
Last edited:
How about using your present suspect plc "input" to energise a standard 24v dc relay which would then switch 24v to your plc input. The relay would be less likely to operate with a small induced voltage.
 

Similar Topics

Hey all, I'm having this issue with an Allen Bradley AC input card(1756-IA16I). I was looking into another issue and found that the inputs on the...
Replies
9
Views
2,969
Hi guys, I'm chasing a strange one here and am trying to eliminate a far fetch theory I have. Background. I have a machine with 5 Micrologix...
Replies
3
Views
2,345
Good Morning , We have about 300' run of shielded 14/4 tray cable (120 vac). We have 2 sensors on a gate, one position trips a sensor , and...
Replies
23
Views
6,088
Application: I have two pumps, a 20 Hp and a 10Hp 3/ph 460v in the same conduit. The Vfd's are located in each mcc bucket. I have been getting...
Replies
5
Views
6,217
A customer of mine has a problem with induced voltage. He has multiple small motors being driven through a multicore cable - I know - should not...
Replies
17
Views
8,601
Back
Top Bottom