Dear All, A very Good morning to all of you,
I was new to this forum and also new in the Instrumentation industry.
I have some problems related to PLC DCS communication request to clarify the same.
I have a control system distributed in three levels Level I is having DCS, Level II is having Main PLC and Level III is having micro PLCs. I have to make communication in between level II to level I (Modbus)and also Level II to Level III(Profibus). Now i was having doubts regarding I/O list of Level II, whether i have to consider all the i/Os of Level III in level II I/O list if the communication is through profibus. and also with level I. Or it will directly communicate with all the levels on communication bus? Also can i read and write any command from level I (DCS) through this communication. waiting for your valuable feedbacks.
 
Dear dnyaneshnawale,

There are several possible solutions. One solution could be to use gateways between the different levels.
Between level I and level II, a Modbus slave to Modbus slave gateway coulde be used. Such as:
http://www.anybus.com/support/support.asp?PID=234&ProdType=Anybus X-gateway
Between level II and level III, a Modbus slave to Profibus slave gateway could be used, if there is a Profibus master present on level III.
http://www.anybus.com/support/support.asp?PID=185&ProdType=Anybus X-gateway

If there is no Profibus master present on level III, you would need a Modbus slave to Profibus master gateway, such as:
http://www.anybus.com/support/support.asp?PID=140&ProdType=Anybus X-gateway

If you would like to have more information about the gateway solution, let me know ([email protected]) or contact our distributor in India.

U L Electrodevices Pvt. Ltd
Nirman Classic, III Floor
Katraj-Kondhwa Road
Pune
411 046
India
Tel: +91 20-26962125
Fax: +91 20-26962079
Email: [email protected]
Webpage: http://www.ulepl.com


//Patrick Lansdorf
 

Similar Topics

Hi Everyone, I am currently trying to communicate ControlLogix PLCs via EtherNet/IP with Delta V DCS. There is a VIM2 card configured for...
Replies
1
Views
270
I am a beginner in automation field i am trying to use DL3500 gateway to establish the modbus communication with Allen bradly PLC and Yokogawa...
Replies
1
Views
2,012
Hi Experts, I have a Siemens PLC inetrfacing with Foxboro DCS. The communication is very slow, takes around 12-15 sec for a DO from DCS to PLC but...
Replies
3
Views
4,307
Dear All, We currently using LG PLC (Type K120S; Model K7M-DR60U). The unit already has built-in RS-485 communication port. This unit then...
Replies
3
Views
5,237
I have created a project in TIA Portal v16 Upd6 with S7-1200 (6ES7214-1AG40-0XB0) and WinCC Unified (PC station). The communication between the...
Replies
4
Views
131
Back
Top Bottom